The Lynx Distributor has a detection circuit with a red or green LED for each fuse. That circuit requires 5 V, which the Distributor does not generate itself.
It normally receives this via the RJ10 connection from a Lynx Smart BMS or a Lynx Shunt VE.Can.
Neither is present in my installation. The Pylontech BMS communicates directly with the Cerbo via CAN, and the DC side is protected with separate MEGA fuses for each branch. As a result, the LEDs remain dark, even though the RJ10 cable between the two Distributors is connected correctly.
The manual states that, for standalone use, you should connect pin 1 of the RJ10 to 5 V and pin 4 to ground. The problem is that this connector is not protected against reverse polarity, and there is no ready-made cable that does this.
Making one myself therefore feels risky. How have others solved this? Has anyone else encountered the same issue with an installation using managed batteries?
System: 3x MultiPlus-II 48/5000, 2x Lynx Distributor M10, 4x Pylontech US5000, Cerbo GX MK2, Venus OS v3.75.