Victron Energy MultiPlus-II - Power Inverter

Can this inverter take 4 cables in AC in (2 hot, 1 ground, 1neutral)?

MP2 3/5k can take 6AWG, the bigger models have M6 bolts

See data sheet and manual

The 240V single phase have an each in/out:

  • 1x phase (hot)
  • 1x Neutral
  • 1x Protected earth

In addition there is one central ground.

I have no experience with the 120V split phase models. Pls download the product manual. It’s all available without registration on the product page.

No. You need two Multiplus-II 120V inverters to make North American split-phase {L1 (hot), L2 (hot), Neutral, Ground}

An autotransformer can give you split-phase 120/240V from a single inverter, but this has serious limitations on neutral current and grounding approach.

1 Like