VE.configure Assistant help

Can anyone advise on how I can get the Assistants correctly set-up to do the following:

  1. AC2 on when SOC 90%+
  2. AC2 off when load 3500w+
  3. AC2 off when SOC 80%-

See image for current set-up. The assistants work well for the SOC parameters but the ‘Off’ command when load is above 3500w does not work. I understand the and/or functionality and how the commands cycle through 1, 2, 3 etc. but cannot see a way to get my no.2 assistant to work.

Thanks.

From the documentation. The way I understand it is if you have an SOC above 91% and the load goes above 3500W for 3 secs the relay will stay on because the on condition has priority. The off condition will only work once the on condition is no longer satisfied, have you tried >3500W after the SOC has gone below 90% but is still above 80%.

Combining multiple Assistants

Multiple Assistants can be used in one unit. For example the Programmable Relay is often used multiple times. When doing so; this is how they are evaluated:

- an ON condition always has priority over an OFF condition - multi criteria in the ON ( or OFF ) list go by the OR principle

Thanks, this is exactly as I understand it but still no closer to finding a solution. I will try using the generator start/stop assistant to operate the AC out 2 as I’ve seen in another post.

You could try
Ac on when above 90% and when load below 3400W.

You tick two conditions to combine them in the wizard.

The off can be separate as that are.