I have a MP2 that I would like the AC output 2 to be active when Battery is above 31% SOC and also when AC input is detected.
Attached is a screenshot of the assistants that I have set up and the behavior is
If the battery is under 29% SOC but AC input is sensed it activates AC output 2.
If the battery is above 31% SOC and no AC input is sensed , AC output 2 in not active.
What I am trying to do is activate AC out 2 above 31% AND OR activate Ac out2 if AC input 1 is sensed.
Any help would be appreciated
On is always priority over off. So if any one of the conditions is met it will be on.
Try to combine two of the on in one assistant (you are able to check more than one box at a time) then both have to be true for it to be on. (AND)
Thank you for that. I am having trouble explaining.
Scenario: pull up at an RV park with less than 29% SOC so AC out 2 is inactive. Plug into RV Park Power and have AC out 2 become active is what I would like to happen. But if NO RV Park power is sensed still turn off AC out @ at 29% SOC and turn back on @ 31% SOC.
The only thing that is connected to AC out 1 is a 230vac fridge. MUST STAY ON ALWAYS.
The rest of the AC outlets in the caravan are active on AC out 2 including air conditioner.
My apologies if this is all vague.
No worries. Its qeird to try to explain sometimes.
Ok. So you haven’t tried it yet?
Ok. Then keep the two on separate so the OR is kept there. Then it is on if either one is true.
Combine the off conditions into one so both have to be true to switch off.
Sometimes just using the percentage conditions alone will be better as ac2 is naturally on when connected to shore. I haven’t used it in a while like that.
Thank you so much for your help.
I could see where you were leading me. I have got it to work exactly how I want it to with the attached assistants. A bit of lying to the shunt on SOC for testing and it works a treat.
Thank you again.