Portal visualisation issue

Can somebody point me in the right direction to solve the below visualtion issue?

Issue: once my PV inverter starts to generate more power than I have loads the “AC Loads” go to 0 and the essential loads (nothing connected to AC OUT 1 or 2) start displaying the sum of the AC loads and the battery charging = total loads. Gateway firmware v3.67. When the PV power < AC loads visualisation is correct though.

I have a second system (below) where the visualisation is correct and I can not find the delta in the settings apart from a Gateway firmware delta v3.64.

Any idea’s?

Where is the PV inverter connected?
You wrote that nothing is connected to AC OUT 1 and 2 but it looks like you configured the PV inverter to be on the AC OUT.

Good point, but not sure where I can specify this (PV is AC coupled on AC IN)

My mistake, during setup of the PV meter (is a meter that simulates a connected PV) , need to adjust in the configuration of the PV dont think I can adjust on the multiplus.

Thanks for spotting this!