Hi, can someone better explain what is the difference between setting up “Grid Current Limit” at inverter settings OR enabling “Peakshaving” on ESS settings?
2nd question: If I need to power boost load at AC-IN side, can any of these 2 features be used? Or only AC-OUT side is supported?
The grid input limit is a continuous limit (never to be exceeded), peak shaving is short term ‘spike load support’. You can set this lower than the grid limit. The grid input would then be the fall back if battery limits are met.
(The limits apply to both - ac in only works if you have a grid meter). And it works well if the grid meter is not slow.