Hmm, so thinking about this a bit more: do the Peak Shaving current limit settings in the screen above only apply if there is a grid meter?
Said differently, if there are only loads on the ‘AC output’ side of the system — so no grid meter needed — then the AC Input Current Limits become the limiting factor for Peak Shaving.
I had a similar situation, there seems to be a bug.
My setup;
MP2 with AC and DC PV, all loads and PV on AC output, no external grid meter (using the internal one)
What worked for me;
Switch grid metering to external (even though there is no external grid meter).
Enable peak shaving and set limit (i only enabled import limit).
Switch grid metering back to internal, the peak shaving settings remain unchanged.
I have not yet checked to see if peak shaving actually works.
I was able to do some tests on a single phase system, one multiplus, with a grid meter installed the peak shaving option works as intended. Without a grid meter you can use the limit AC input current in the inverter settings. This is of course different from limiting the total input power when using multiple inverters.