Grid current limit exceeded with DESS and peakshaving on

I set both grid current limit and peakshaving on at max. 25Amps. But still the grid current exceeds 25Amps. That is worrying. What goes wrong?

When I turn off DESS, the current limit decreases under 25Amps.
Afbeelding van WhatsApp op 2024-08-31 om 14.07.04_3ff0acfc
Afbeelding van WhatsApp op 2024-08-31 om 14.07.10_3d760011

Also with DESS off and Keep Batteries Charged, the current limit is exceeded as well.

There is load on AC In and AC Out1. A VM-3 us used as grid meter

UPDATE: with this setting, it does not exceed
Afbeelding van WhatsApp op 2024-08-31 om 14.19.24_34ae1e1c

We experience the same, any solution yet?

See if it’s not due to the load current coming from the grid
to reduce the diffirence, I had reduced the charging current come from the grid

If it was related i dont know.

I stil had this going on with the latest Venus OS beta
Settings > System Setup > ESS > Peak shaving
Peak shaving ‘Always’
‘Limit system AS import Current’ switched off
‘Limit system AS export Current’ switched off

After switching both on en set the current to 26Amps on both options it works like a charme.