I have a orion xs50 (firmware 1.12) which give error 161.
The errror is showing on the touch screen, sadly not in the VRM alarm logs.
Same error was also with version 1.11
In VRM it is visible, that Orion XS, keep charging continious 50amp.
It only give the error and keep working as normall.
The error pops up ones in a week.
My dealer responce is, “post it here”.
Any one a suggestion how to solve this?
I think R&D needs to know this problem, but how to reach the R&D team, if the dealer ask to post it here?
I have the feeling that something in the monitoring a short cut is to sensitieve and gives false error 161.
cables to busbar only 0.5 mtr is 16mm2.
busbar to 600Amp lifepo, is 0.5mtr 70mm2
Cable resistant and Lifepo4 resistant is very low. If there is a shortcuit protection, maybe it is triggered to early becausse this very lwo resistant.
Temperature: not higher as 40degrees.
ALSO suggestion to R&D, can the errors on the touchscreen like 161, also reported to the VRM/alarm logs.
I have the same problem. #161, #28, and #21
It won’t charge, it stays at 0. I turn off the Orion in the app, but it keeps heating up.
The seller hasn’t responded in 3 weeks. This is poor service and a bad image for Victron.
there was an issue with Version 1.07, which resulted in „heating up“ and „Short circuit“. This is Not know to be a Problem with 1.12.
Here the Infos about 1.07
v1.07 – 9 December 2024
Known issue
When the battery voltage gets above the output voltage target, there is a chance that the Orion XS will generate an internal short and fail. Error #28 might be triggered in such a case, which is an indication that the charger is faulty.