Offgrid MP2 15000 + Autotransformer 240/120v and can't get MP2 to engage the Ext Gnd Relay

I have an off-grid setup in the US with a Multiplus-II 15000/230v wired to the Victron Autotransformer (100a) and can’t get the MP2 Ext Gnd Relay wires to engage the N<>G relay at the autotransformer to bond split phase N to G vs the MP2 bonds 240v N to G. In this split phase setup you can’t bond N or L at 240 on the MP2 to ground and the way I have it wired matches https://www.victronenergy.com/upload/documents/Datasheet-Autotransformer-32A-and-100A-EN.pdf Figure 1: Split phase supply for unbalanced load (Ground relay of autotransformer should be used)

Two test scenarios i’ve done, both not working as suppose to…

  • Manually provide 24v to the auto transformer and the yellow light turns on showing N to G/PE its engaged, fluke meter confirms, voltages are good and powers the house just fine, including GFCIs. VE Config / Grid profile is Other:AC Neutral path externally joined (VE Config / Inverter tab shows Ground Relay not checked, which means should be disabled)
  • Setting grid profile to Other: Not compliant to any grid code standard (VE Config / Inverter tab shows Ground Relay enabled) - The MP2’s 240v N is bonded to G and not seeing 24v at the Ext Gnd Relay or even a flicker when wired to the Autotransformer and its on too incase its sensing for continuity for internal/external. (Autotransformer obiously not wired with ground to test to prevent conflicting 240v N to 120v N getting cross/bonded if both relays engage. Apparently the newer MP2s should auto select internal vs external if external is wired? I have no DIP SW1’s internally I can find to turn on/off unless I missed them.

Is there a setting I’ve missed either physically on the MP2 or Autotransformer or in VE Config to enable the use of the external ground relay and disable the internal relay?

This isn’t exactly the scenario described, but I too use an MP2 (8kVA 230V) with Autotransformer in N.A. to produce 240V split phase. In my case, N - G bond is in my main load panel, so MP2 ground relay is disabled, as is the Autotransformer ground relay.

External AC is provided by a Honda EU7000is, with the L1 and L2 connected to L and N on the MP2 AC input. The Honda’s Neutral is not connected.

The system works without a hitch.

Which grid profile are you using? I assume Other: AC Neutral path externally joined and not using the internal or external relay and also not using the auto transformer relay too, right?

When I do a generator, it only accepts the “grid” when I use Other: Not compliant to any grid code standard which when generator is off, the MP2 bonds N<>G. The externally joined profile switches on/off of the generator like its unacceptable under this profile, which makes 0 sense. Its a GenMax inverter style generator 10.5kw and if its set to full speed or variable speed control, doesn’t make a difference. Only errors I see in my CerboGX is grid lost. Is there a deeper level of logging I can see like not able to sync frequency or ground fault or something else?

Your setup is similar, I’d like to have a generator as backup during summer months and weeks with bad weather… Likely pulling the trigger on 25kw Generac with 250gal diesel belly tank, but thats “phase 2” :slight_smile: That will be grounded once installed, likely similar to my existing problem.