External Transfer Switch - Multiplus 8, 10 and 15kW

I am trying to get my head around the new External Transfer Switch method used to parallel the 8, 10 and 15kW multiplus 2.
Overall, it looks like a great option with reduced AC wiring, Multiplus rather than the more expensive Quattro and they fact that we would no longer need a bypass switch.
My understanding so far:

AC Out is used for all Power, In and Out
Special firmware needed
Both 3 phase and Parallel configuration
AC In is just used as a voltage sense input, so only needs to be 1.5mm2
Both Grid disconnect and Earth-Neutral bond is via external relays in this configuration
Will operate as Off-grid (no grid code) and ESS (with grid code)

I have a few questions for anyone that has done this:

  1. A 20 meter limit is suggested between meter box / main distribution point and the Multiplus setup. Is this due to the voltage sense and/or current transformer measurement cable length restrictions? If so can a ET112 be used to over come this, and if so for V and I?
  2. Will functions like, ’ignore AC in’ to force the system off grid as needed still work?
  3. Will item (2) above work with Generator Assist as a workaround for scheduled charging

Thanks for any input,

Simon…

I have now drawn this up for a single phase 2 x 15k Multiplus. Looks good, the 20m limit is a pain, this is due to the current transformer [I could do with 30m].

Any real world feedback from anyone, especially the change over time between pass through grid connected to inverter power and back to grid pass through? Using the internal relays its pretty instant, same for the external?

Thanks,

Simon…

Unfortunately no feedback.
I am also in need of knowing if the CT is obligatory for external transfer or if an external power meter can fulfill the ‘CT’ measurement.

This would take away the 20m max restriction for the CT cable.

I have a feeling these will be too slow.
It is a common complaint even in normal ESS applications