Before I will order the Ziehl, I had recently set up a test system with the S99 firmware in a 3-phase setup.
The master unit uses the Aux Relay to switch the External Relay.
I encountered a phase rotation issue between the phases, which initially prevented two of them from synchronizing.
I adjusted the phases to a clockwise phase rotation, after which the phase synchronization was successful.
You can monitor this process via VE.Configure for the VE.Bus system.
The MultiPlus system syncs the phases, and internally (on the master unit), you hear the Aux Relay trigger for a very brief moment.
This process repeats itself. I could hear a ‘changing, faint buzzing’ sound indicating that the phase syncing checks are being performed, and after a short delay (or “after a few cycles”), it triggers the Aux Relay again.
You can see a small time bar on the VE configure monitoring screen during this.
This process repeats as long as the External Relay fails to connect the Grid to the Victron System.
Is this mechanism designed to ensure that a very quick-responding Relay is used?
How much time does this external Relay have for connecting the Grid, so the Aux Relay keeps the signal on?
The CT measurement is also used in the algorithm to determine if the External Relay should be open.
If current is still flowing (when it shouldn’t be), it results in Error 24, and the system enters a safe mode.
I will set up the test system again with a separate relay to gain further insight.
20250902
Remote Transfer Switch application works as intended, at 26.5m distance from the fuse box.
Not even a blink is visible, you wouldn’t notice if the grid disconnects also the SMA Tripower x15 keeps running without interruption and power decrease. After switching the Grid back on the voltages are different and therefor the PV overproduction flows into the Grid the moment the contactor closes.
Also noticing that PV power regulation gets very slow adjusted to load the batteries.
Don’t know if this is a bug or something from the SMA / Multiplus combination.
Need to do some more testing with grid interruptions.
Components
- Contactor 4p 100Amps.
- Signal cable 26.5m for the contactor.
- 4x1.5mm2 signal cable for the phase syncing on all three Multiplus AC Input.
- 4p 6Amps fuse for the Syncing signal cable.
- 3x CT Clamps, wired with 26.5m UTP (SFTP would be better).
- 5x6mm2 between fuse box and the three 8kVA Multiplus installation with C32 fuse.
- Ziehl is ordered.
The rest of the electrical installation is as before secured with RCD’s and some parts with RCBO’s.
After receiving the Ziehl i will install it as required in NL and put the ground relay in place.
Firmware updates do interrupt the complete installation as the contactor will be off.
You can build a bypass with a second relais with auxiliary contacts to prevent bad things.