I been crunching some numbers with the Victron setup below and there are some issues…
Hypothetical setup…
60 AIKO STELLAR 2N+78 (AIKO-A805-GRH78Dw) 805W (48.3kw)
2 Victron Quattro 10kVA 120V QUA483100102 inverters connected in parallel.
10 Victron SmartSolar MPPT 250/100-Tr VE.Can
Victron Cerbo GX MK2
6 Coremax 20 kWh 48v/400ah battery banks. 120kWh usable storage.
Running the numbers through ChatGP, it says that the MPPT controllers are not the problem and they can handle the solar array 48.3kw and there is no clipping with the MPPT controllers. But, massive clipping occurs with the inverters and there is a huge bottleneck with inverters and battery charging…
Inverter-Limited Clipping
-
Your 20 kVA inverter bank can handle up to ~20 kW AC.
-
Your 48.3 kW DC array can produce far more than this under ideal conditions.
-
Even with Alaska’s lower annual insolation, short winter days with high solar reflectance from snow can lead to peak DC output exceeding 30–40 kW.
-
Result: Significant clipping at the inverter stage when DC > 20 kW.
For example, at 80° winter tilt and snow cover, panels may produce 70–80% of rated capacity during midday. That’s ~38–39 kW DC, far exceeding the 20 kW AC inverter limit.
Battery Charging Limit
-
Coremax 20 kWh batteries: Assume max charge rate of 0.3C = 6 kW per unit → 36 kW total.
-
But your inverter/charger limit (Quattro 10kVA each) caps charging at ~150A @ 48V = 7.2 kW per inverter → 14.4 kW total.
-
Bottleneck: Even if solar and MPPT can deliver more, battery charging is limited to ~14.4 kW.
To eliminate this, I would need 7 Victron Quattro 10kVA 120V inverters: Roughly around $20,000 dollars just in inverters only.
7 Victron Quattro 10kVA 120V inverters: $20,000
10 Victron SmartSolar MPPT 250/100-Tr VE.Can $6,130
2 Victron Orion-Tr Smart 48/12-30A (360W) Isolated DC-DC Converter $488
Victron Energy Cerbo GX MK2 $248
60 AIKO STELLAR 2N+78 (AIKO-A805-GRH78Dw) $5,000
6 Coremax 20 kWh 48v/400ah $15,000
Total: $46,866