Hi Tom
thanks for the input!
I use around 25Kwh per day. I mostly get by on the Pylontechs (around 29kwh) with solar as well
I have a spreadsheet showing consumption and generation, if itās of interest? I have data going back several years, but only just on a year for the current setup.
The pricing for electricity here is very different from the UK, the first 300 units per month are the cheapest after that the cost rises dramatically. The local property tax is also related to your energy consumption and again that rises dramatically when you use more than 300 units a month, so there are major incentives to be as frugal as possible:-)
Peak loads are for cooking using an Induction hob, fan electric oven, in the summer thereās some some 15Kw of airconditioning. Very occaisionally thereās also a 4Kw immersion hetar, but 95% of the time thatās taken care of by solar heating and in the winter thereās an indirect coil attached to my pellet boiler, that adds to the base load in the winter, right now (17.45) the base load is around 435watts, made up of the pellet boiler, two freezers, a fridge, power for the internet via StarLink, some lights, all of which are LED.
Thereās also a washing machine (1.2Kwh per load), dishwasher (0.8Kwh per load) and the usual collection of kitchen appliances, kettle, (3.0Kw) air fryer (1.4Kw) microwave (1.0Kw) being the other big consumers of units.
My current system is setup as follows:- Solar First with battery charging first priority, then battery and finally grid. From March until the beginning of October my grid consumption is minimal, it averages around 0.5 unit per day, November to the end of Feb it rises to around 5-10 units a day but is very weather dependent, We normally manage round a day and a half on battery/solar if the weather is cloudy. In the summer he batteries are normally fully charged by mid morning.
Distributing the peak loads is done as a matter of course, especially in the winter 
The peak load is probably from the hob at around 7.5Kw, but usually much less.
I started with a 5Kw solar inverter/charger, then went to two of them in parallel (both badge engineered Voltronics units) Coupled to 4 x 2.4KW Voltacon Solar llithium iron phosphate batteries.
Throughout there has always been problems with communications between the charger/inverters and the BMS in the batteries, along with endless firmware problems. On the failure of one of the 5Kw units last year I swapped to a Axpert 11Kw Max-E (also a Voltronics unit), running 18 panels in two strings of 9 panels, it was advertised as having a BMS with a setting for Pylontech Batteries, sadly that turned out to be only partially true.
No I donāt want to feed back into the grid.
I probably donāt need an 11Kw inverter (my grid connection only supplies 40A of single phase) 8Kw is probably enough. I know that matching the inverter size to the demand is important for efficiency, but as sometimes temperatures top 43degrees here I feel that having a large inverter running conservatively will be more reliable than one running at near maximum output?