System is all wired up Multiplus II, Cerbo GX MK2 and Lynx Smart NG. The batteries arrived and all hooked up. The invertor is not working and amongst other alarms (relating low battery, low cell voltage, state of charge) I get a VE.Bus Error 15 alarm. The multiplus is blinking “bulk” and “inverter on” and doing a cycle. There is no charge voltage appearing on the inverter. This is all telling me BMS (via Cerbo) is not talking to the Multiplus. I have cheked the rj45 cables and have the ve.can rj45 terminations are installed. All of the firmware is up to date. Please help with some idea on what to do next as I am stuck !
I found that but not sure where to go next with it. The batteries are victron Lifepo4 NG and Lynx Smart BMS NG. How do I verify if the cerbo can port is set up correctly? The system came from a distributor so in theory it should all be configured and ready to go.
Okay, I am told that the SOC is too low and the inverter is not interested for this reason. I need to charge the batteries and the problem will be solved. I have ordered a charger so will have an answer in the next 24 hours.
I am also told the ve bus alarm is spurious and will clear up when I get the batteries charged up. Let’s see…..