As above I need to find a manual for the Easy Solar 48/5000/70 with GX Colour control onboard - it has a 150/100 Mppt onboard. I cannot find this manual ANYWHERE and I have hunted high and low. The dealer simply says go to the Victron website. The Victron website DOES NOT SHOW a manual for this version - for the 12 or 24v version of this model - yes. But for the 48v model - nothing at all.
OK so where I am confused is that there are 3 x sets of PV inputs - the installers only used 2 sets of inputs - currently there are 12 x 330w panels -
(although we had to replace a broken panel with a 320w panel as it is the closest we could find to the 330w panels these days - so I guess its now 12 x 320w panels?)
The data sheet says we can go as high as 5800w of PV input (but that is at 58v and I only go as high as 55.4v) - I want to understand how these 3 PV inputs are wired to the Mppt - dont want to damage anything -
I want to over panel the PV inputs as we are in our rainy season so PV production is low - looks to me that the installer has done 3 panels in series and then those 3 panels paralleled thus taking up one set of the PV inputs on the Easy Solar and the same on the second set of PV inputs on the Easy Solar - seems like we could replicate that same set of 3 in series and 2 sets of those 3 in parallel to max out the PV connections on the Easy Solar - but what if I over paneled that third set of PV inputs (NOT going over the Voltage limit of 150v - but I believe that going about 30 to 50 amps over the 100 amps is fine?)
Of course if I over panel to some degree it will just clip in clear sky conditions but it would be a massive help in our rainy season we are in now.
So this is why I wanted to get the manual for this EasySolar 48/5000/70-100 150/100mppt unit.
One other thing I want to understand - on that third set of PV inputs at the bottom of the EasySolar unit - is that a separate tracker ? If so I could put another set of 6 x 320w panels facing direct EAST (the 12 installed all face the same way - North) - that way I can soak up the morning rays - its usually sunny in the morning a lot of days but gets very overcast around midday and rains most afternoons - so a definite benefit to get some panels facing East?
If I cant do that on the 3rd set of of PV inputs then I guess my next option is to add a standalone Mppt?
(this install was done about 7 years ago - not by me - and the installer is no longer interested in his old installs - only getting bucks for new work)-
They are on a shared bus bar internally.
Each mc4 connector has a current limit of 30A. So it is possible that the pairs on each is under the limit when parallel connected.
It is one tracker. So matching strings and voltage same facing roof/mounting is essential
If you want to add more panels it is best to add a another mppt for best performance. Especially since the panels will be different in model and spec.
Correct the big older easy solars are the âold multiplusâ
The MP2 has the same continuous power. The peak duration is a bit different. I have used both and been happy with them
The only time i prefer the older MP is when the conditions for the install require that cooling be a priority as they have a bigger body and fans etc. but then we donât have grid code regulations so strict to require the double disconnect of the MP2.
For the pump it will depend on what kind of start load it is (for both models). If the start circuit is in good condition i donât see why the newer model would not be able to do the short duration peak to get it started. Running would not be an issue since it is within the continuous rating of the inverter.