Problem: ESS doesn’t seem to be working as I expect (I’m not using DESS). The battery is still being charged in the evening (when there is no AC-PV production) from the grid. I expect this to happen only during the day when AC-PV is available.
3-phase grid connection, 1 x Multi RS Solar (connected to L2), VM-3P75CT, Cerbo GX, AC loads on AC-out and AC-in.
Question: With ESS on the MRS, is a single connection to L2 supported, or does it always have to be L1?
Interestingly, and I don’t know whether it’s important, all the screens in VictronConnect are black and white, not blue and white.
Today I installed the VM-3P75CT and connected it to the Cerbo GX via VE-Can; the Cerbo GX is connected to the MRS. VM-3P75CT: v1.11, MRS: v.1.24, Cerbo GX: v3.85
I clamped the three CTs around the three phase wires. Role: grid meter, phase config: 3-phase, registration: vector.
Interestingly, the phase sequence appears to be L1-L3, L2, whereas I expected L1-L2-L3.
Also noteworthy: in the VM-3P75 manual, under “settings - C Settings”, it lists Role, phase configuration and position. In my settings screen I can see role and phase configuration, but no position.
The values from the VM-3P75 that I see in VRM seem realistic.
What I’ve already done:
- VM-3P75: factory reset; checked several times that the CTs are around the correct phases and connected to the correct inputs: CT1, CT2, CT3.
- Checked that L1, L2 and L3 of the VM-3P75 are connected to the correct phases.
- Rebooted the Cerbo GX.
- The values in VictronConnect from the VM-3P75 seem correct.
- Checked the VE-Can bus: lots of data packets, no errors
Observation
During the day, while AC-PV was producing power, I noticed several strange things, but for now I’ll limit myself to one aspect.
Now, in the evening, when the AC-PV inverter isn’t supplying power, the battery is still being charged from the grid. I expect the battery to be charged only during the day, using AC-PV power.
As soon as I lower the input current limit to 0.1A, the battery stops charging (as expected). The AC loads (on AC-out) are then powered by the battery.
It must be a configuration error, but after checking five times, I can’t see anything wrong. I must be overlooking something.
General:
- mode: on
- energy meter support: on
Grid:
- EU
ESS:
- mode: optimized without battery life
- grid setpoint: 0 W
System:
- standalone
- phase selection L2
- prevent CAN network islanding: on
Remote console settings:
System setup:
- AC input:grid
- position of AC loads: AC input & output
- opportunuity loads: off
- battery monitor: RS 48/6000/100
- DVCC: off
- Venus Large, but no active flows
All System instances are set to 0
No scheduled charge levels
I’d really appreciate your help.