MultiRS: ESS, battery is being charged (from the grid) despite no PV production

Problem: ESS doesn’t seem to be working as I expect (I’m not using DESS). The battery is still being charged in the evening (when there is no AC-PV production) from the grid. I expect this to happen only during the day when AC-PV is available.

3-phase grid connection, 1 x Multi RS Solar (connected to L2), VM-3P75CT, Cerbo GX, AC loads on AC-out and AC-in.

Question: With ESS on the MRS, is a single connection to L2 supported, or does it always have to be L1?

Interestingly, and I don’t know whether it’s important, all the screens in VictronConnect are black and white, not blue and white.

Today I installed the VM-3P75CT and connected it to the Cerbo GX via VE-Can; the Cerbo GX is connected to the MRS. VM-3P75CT: v1.11, MRS: v.1.24, Cerbo GX: v3.85

I clamped the three CTs around the three phase wires. Role: grid meter, phase config: 3-phase, registration: vector.
Interestingly, the phase sequence appears to be L1-L3, L2, whereas I expected L1-L2-L3.

Also noteworthy: in the VM-3P75 manual, under “settings - C Settings”, it lists Role, phase configuration and position. In my settings screen I can see role and phase configuration, but no position.
The values from the VM-3P75 that I see in VRM seem realistic.

What I’ve already done:

  • VM-3P75: factory reset; checked several times that the CTs are around the correct phases and connected to the correct inputs: CT1, CT2, CT3.
  • Checked that L1, L2 and L3 of the VM-3P75 are connected to the correct phases.
  • Rebooted the Cerbo GX.
  • The values in VictronConnect from the VM-3P75 seem correct.
  • Checked the VE-Can bus: lots of data packets, no errors

Observation
During the day, while AC-PV was producing power, I noticed several strange things, but for now I’ll limit myself to one aspect.

Now, in the evening, when the AC-PV inverter isn’t supplying power, the battery is still being charged from the grid. I expect the battery to be charged only during the day, using AC-PV power.

As soon as I lower the input current limit to 0.1A, the battery stops charging (as expected). The AC loads (on AC-out) are then powered by the battery.

It must be a configuration error, but after checking five times, I can’t see anything wrong. I must be overlooking something.

General:

  • mode: on
  • energy meter support: on

Grid:

  • EU

ESS:

  • mode: optimized without battery life
  • grid setpoint: 0 W

System:

  • standalone
  • phase selection L2
  • prevent CAN network islanding: on

Remote console settings:
System setup:

  • AC input:grid
  • position of AC loads: AC input & output
  • opportunuity loads: off
  • battery monitor: RS 48/6000/100
  • DVCC: off
  • Venus Large, but no active flows

All System instances are set to 0

No scheduled charge levels

I’d really appreciate your help.

I’d first try updating the Multi RS to the latest firmware version. Quite a few things have changed in the meantime for ESS between v.1.24 and v.1.31.

@limwakra
I was hesitant to upgrade.
I couldn’t see anything in the release notes that related to my problem either.

But I went ahead and upgraded anyway.
And guess what?
Yes, yes, it seems to be working.
So far, everything is as expected.
Tomorrow I’m curious to see if the AC-PC starts supplying power, but I’m confident it will.

Thanks for the encouragement.

I still find it strange that my VictronConnect screens are black and white; everywhere I look, I see blue and white. Strange…

Normally it’s recommended to not upload unless you have problems.
If you have problems an update should always be the first thing to try.

VictronConnect got a dark mode a few months ago.