Hi
if you use a clamp, the setting related to the current sensor must not be changed (and thus, remains “internal”) as the clamp is actually connected to the same (internal) sensor connector on the multiplus.
External current sensor setting must only be used for really external meters, not the CT clamp connected to the MP2 connector.
Matt