3-Phase system with parallel MultiPlus II and external CTs — current reading exactly double

Hi everyone,

I’m running an ESS system and need help with an external current sensor issue that’s causing exactly double current readings on a 3-phase, parallel MultiPlus II setup.


:small_blue_diamond: System configuration

  • 3-phase VE.Bus system

  • 2 × MultiPlus II 48/3000/32 per phase (6 units total)

  • Each phase master has an external current sensor (CT) connected

  • CTs are located right after the grid meter, before splitting to the inverter pair

  • VE.Configure: “External current sensor connected” enabled on each phase master

  • ESS Assistant active (grid-connected mode)

  • INT–COM jumpers removed on all slaves — leaving them in caused power measurement errors

  • Cerbo GX + VRM monitoring

  • 3-phase AC-coupled PV on AC-OUT, but problem existed before PV connection


:small_blue_diamond: Problem

  • Grid current (A) shown on Cerbo GX and VRM is exactly double the real value (verified with clamp meter)

  • Power (kW) readings are correct

  • ESS grid-limit and set-point must be multiplied by 2 for the system to behave normally

  • It seems the current from each phase’s CT is being counted twice — maybe by both master and slave, or by VE.Bus aggregation logic


:small_blue_diamond: What I’ve checked


:small_blue_diamond: Questions

  1. In a parallel MultiPlus II setup (per phase), what is the correct configuration for external current sensors so that only the master’s CT is used in ESS calculations?

  2. Should slaves keep the INT–COM jumper (internal CT) or should it be removed when the master uses an external CT?