Hi everyone,
This might be a long post to convey all the information needed. For disclosure, I am a licenced electrician, however this Victron system is a hobby for myself, and my day-to-day job does not involve installing and commissioning them.
The installation and backstory:
- 3x MPII 10k in three phase 230/400V configuration.
- DC coupled solar only (2x MPPT 450s)
- Ekrano
- Battery Shunt
- Custom LifePo battery bank – BMS’s currently not wired / configured to talk to Victron system currently.
The wiring configuration is not ideal given the location of the MPs in relation to the incoming grid / MEN connection and the outgoing circuits from here. It is not laid out how I would prefer it to be, but given existing infrastructure, limited room in the main switchboard etc I designed it this way.
A basic description: The house contains the main switchboard where the DNSP termination and meter is located. From here a grid supply to ‘Shed 1’ is provided where the system is situated. The MP’s then supply their inverter output to a change-over switch where the entire properties loads are supplied from (either the MP’s or grid). After the change-over switch I have three main submains: A 3phase supply on a separate cable is sent back to the house to feed all the house circuits, A 3phase supply to ‘Shed 2’ and a 3phase supply the distribution board for local loads in ‘Shed 1’. The Victron power meter is situated in the main switchboard adjacent to the retailer meter.
In Australia, we can only have 1x MEN (Neutral-Earth Bond) throughout the installation which must be located at the main switchboard where the DNSP terminates.
This means that the MPs are down stream of the MEN and in my case, they are in another building.
We can have multiple MENs under certain circumstances and installations but for the sake of this discussion on a residential property, there is only 1x allowed.
I will provide a drawing of how it is laid out and wired and post it shortly.
The system has been working very well completely off grid for a year now with no issues.
Current story and issues that unfolded last night:
Coming into Australian winter it was time to get the system onto the grid for when solar input is insufficient, especially now that I have the entire property running off the MP’s inverter to be off-grid as much of the year as possible. With priority of self-consumption from solar and the battery, only using the grid in certain conditions:
- SOC <15%
- Charge batteries to 90% during a daily time slot for 'cheap or free power from the grid
- Never feed into the grid
I Setup ESS assistant in each of the MP’s. with the below settings:
- System uses LiFePo4 with other type BMS
- Battery Capacity 1120Ah
- Sustain voltage 50.00V
- Dynamic cut off – 0.005C – 50.00V, 0.25C – 49V, 0.7C – 48.2V, 2C – 47.5V
- Restart offset – 1.2V
- PV inverters – No
MP main settings
General
50Hz, Shore Limit Input – 40A. Overruled by remote - unticked, Dynamic Current limiter - Unticked, External current sensor connected – Unticked, Enable battery monitor – Ticked, SOC when bulk finished – 95%, Battery Capacity – 1120Ah, Charge Efficiency – 0.95
Grid
Grid code: Australia A: AS/NZS 4777.2:2020 Standalone App. M (no N-bypass), AC Input related settings – Above selected gridcode plus LOM B (compliant)
Inverter
Inverter output voltage – 240V, Ground relay – Ticked but greyed out, DC Input low shut-down – 47V, DC Input low restart – 51V, DC input low pre-alarm – 48.5V, Do not restart after short circuit – Unticked, Powerassist – Unticked, Shut-down on SOC – Unticked, Enable AES – Unticked
Charger
Enable charger – Ticked, Weak AC input – Unticked, Stop after excessive bulk – Unticked, Lithium batteries – Ticked, Configured for VE Bus BMS – Unticked, Disable VSense – Unticked, Charge curve – Dropped current to 75A.
Virtual Switch – disabled
Assistants - ESS
Once I believe I had the settings correct, I switched on the grid to the MPs, they began chattering their relays several times in sequence then appeared to sync to the grid for a brief period of time before disconnecting again. System then appeared to attempt re-sync every 1-minute which lines up with ESS settings.
Looking at IP issues log, input voltage was flagged as too high on the unit which I found bizarre as it is verified as acceptable.
Looking further into it, I noticed that the grid code was set as Australia A AS4777:2020 M (No N-Bypass). Now as I do have a physically wired Neutral bypass where the MP input and output neutrals are tied together, I thought this was odd and that I must have selected the wrong grid code when initially setting up the units and that this might be the reason the MPs are not syncing to the grid.
Changed grid code to Australia A AS4777:2020 M (With N-Bypass) after finding the correct password and sent the change to the units. Upon the MP’s powering up again I experienced some very odd, and unfortunately damaging behaviour. When they powered up a ‘surge’ for lack of a better word or understanding has occurred at the house damaging certain equipment. The MPs were on for about 5 seconds before I immediately isolated the output isolator from the MPs after I noticed some of the outdoor lights rapidly flickering, and upon further inspection damaged smoke alarms in the house and an RCD on L3 in shed 2 had tripped.
The damage: Multiple smoke detectors in the house were damaged, along with 1x or more external PIR light detectors and several phone chargers.
I am yet to investigate this in detail and understand the damage – I have a feeling that there might be a phase cross issue across the lighting circuits where the smoke detectors are on separate phases (and RCDs) yet have an interconnection wire between them.
NOTE – The grid input to the MP’s was isolated at this time. Grid was energised and live to the meter board (at the house) powering only the Victron Grid meter and Grid surge diverter. It is worth noting that the grid Neutral is still ‘live’ and physically connected to the MPs input and output Neutral – All neutrals throughout the property must be permanently connected with none switched as required by Australian Wiring rules.
I changed the grid code back and resulted back where I was, albeit with some device damage.
Looking at the settings again today, it appears that the ground relay is still in used – it is ticked but greyed out, my understanding is that the MP should disable the ground relay when using an Australian grid code where the neutral earth bond (MEN link) is done as a permanent link in the main distribution board.
I need to get some guidance on what issue(s) I am potentially facing here. I completely understand I may have a hidden wiring issue and/or entered incorrect settings. However, as I am in a steep learning curve on this I may miss considering other aspects.
What I believe is wrong in order of likelihood:
- Ground relay not disabled
- Configuration / setup
- Imbalance / harmonic issue between the main switchboard and the MPs (Grid Neutral and MP Neutral are essentially shared)
Questions:
- What do the two grid codes specifically do to the Multiplus input / outputs? In some way, changing the grid code has caused a short circuit or surge of some description from phase to neutral or even phase to phase.
- Ground relay operation, I need to ensure this is completely disabled under all circumstances, whether on grid or off grid.
- What may I have configured wrong?
- What should the correct operation of syncing to the grid look and sound like? Logic says to me that the MP grid relays should all close at the same time upon syncing and that’s it.
I will start doing some basic checks now:
- Incoming grid voltage
- Incoming grid phase rotation
- Incoming grid phases are wired to the correct MP L1-L1, L2-L2, L3-L3
- Neutrals are connected and all tied together.
- MP Active and Neutral input not reversed.
Regards,