Multiplus 2 Will Not Feed In
Just installed a MP2 grid tied, have setup ESS and works when the system grid tied solar is running. Maintains the net close to set point when charging batteries.
Issue is the MP 2 will not export, have been over all settings and nothing is jumping out at me. Hoping have missed something here.
Summary of Settings
TAB: General
System frequency 50Hz
Shore current 15.0 A
Overruled by remote unchecked
Dynamic current limiter unchecked
External current sensor connected (see manual) unchecked
State of charge when Bulk finished 95.0 %
Battery capacity 78 Ah
Charge efficiency 0.95
TAB: Grid
Country / grid code standard Australia B: AS/NZS 4777.2:2020 stand alone app. M (no N-bypass)
AC input 1 Above selected gridcode plus LOM B (compliant)
TAB: AS/NZS4777.2:2020 Australia B (Stand alone appendix M)
Volt-Watt curve voltage V1 195.0 V
Max charge power at V1 0 %
Volt-Watt curve voltage V2 215.0 V
Max charge power at V2 100 %
TAB: Inverter
PowerAssist unchecked
Inverter output voltage 240 V
Inverter DC shut-down voltage 50.20 V
Inverter DC restart voltage 52.20 V
Low DC alarm level 51.20 V
Do not restart after short-circuit (VDE 2510-2 safety) unchecked
enable AES unchecked
TAB: Charger
Enable charger checked
Weak AC input unchecked
Stop after excessive bulk unchecked
Lithium batteries checked
Disable VSense (for diagnostic purposes) unchecked
Configured for VE.Bus BMS unchecked
Charge curve Fixed
Absorption voltage 57.60 V
Float voltage 57.60 V
Charge current 39 A
Repeated absorption time 4.00 Hr
Repeated absorption interval 7.00 Days
Absorption time 4 Hr
TAB: Virtual switch
TAB: Usage
Virtual switch usage Do not use VS
TAB: Assistants
TAB: Assistant Configuration
ESS (Energy Storage System) (size:1012)
*) System uses LiFePo4 with other type BMS
(This can be either a BMS connected via CAN bus or a BMS system in which the
batteries are protected from high/low cell voltages by external equipment.)
*) The battery capacity of the system is 78 Ah.
*) Sustain voltage 48.00 V.
*) Cut off voltage for a discharge current of:
0.005 C= 50.20 V
0.25 C= 49.50 V
0.7 C= 48.00 V
2 C= 46.00 V
*) Inverting is allowed again when voltage rises 1.20 V above cut-off(0).
*) Relevant VEConfigure settings:
- Battery capacity 78 Ah.
- PowerAssist unchecked
- Lithium batteries checked
- Dynamic current limiter unchecked
- Storage mode unchecked
Silence fan (size:46)
*) Disable fan during charge, when Auxiliary input 1 is closed.
Total size of all assistants including the required
(hidden) system assistants is: 1119
TAB: Advanced
limit internal charger to prioritize other energy sources unchecked
@stuartscott171
Feed in settings are found on the GX device under
Settings- ESS
Have attached a screen shot with those feed in settings.
I am wondering if this has something to do with my grid energy meter. EM340 → RS485 ethernet → Cerbo, have written a custom .py file. Being my first installation I am not sure what is normal behaviour.
The meter appears to be functioning, shows under devices and values are present.
And the grid meter is in the correct position as well? Is it metering grid or PV?
If you remove all customisation does it work?
Did it work before customizing? What AC PV do you have? Is it on the input or output?
Grid meter is installed in correct location, reason for the customisation is main switchboard location and MP2 are two different buildings with only optical fibre between them.
As EM340 is supported with RS485 direct it might be worth I try running a temporary copper pair and testing. if only to eliminate this being the issue.
So you are aiming at feeding past the meter?
As a short test are you able to move it closer (it might be less work - obviously I don’t know all the details of your install) and try the feed in that way? Then move it back if it works and troubleshoot after?
Have attached a simple diagram showing the layout, Building 2 is new and has been used as battery storage location where Building 1 is the existing electrical installation and main feed in point.
Effort will be easier running a twisted pair 30m.
Idea is to use Building 2 as essential fridges/freezers running of AC-OUT, then be able to charge of Building 1 solar system then supplement (Net zero) feed-in during night hours.
Have you already taken into account to connect the energy meter via Zigbee?
To be honest only just discovered those tonight. Has put me in two minds now, use the zigbee solution or replace the grid meter with a Victron (provides ethernet and much faster update rate) pricing is very similar.
This still hasn’t ruled out my original problem, bad ESS configuration or meter connection.
A temporary cable, just for testing purposes, could be an option. It would help you in differenciating between grid metering or configuration as the possible sources.
Will give running a temporary cable a try over the next week, will report back any findings.
Thanks for the assistance :smiling_face:
I’m also seeing a similar issue with my 3x 5000VA 48V MP2s in three phase where the MP2s are not feeding excess solar into the grid and are instead frequency shifting and lowering the power output of my Fronius inverter and eventually shutting it down with a high voltage.
My Fronius Symo 15kW inverter is set to MG50 grid code and my Victron MP2s are set to AS/NZS 4777.2:2020 stand alone app. M (no N-bypass) grid code. AC-Coupled Feed in is enabled in ESS and my Fronius inverter is wired into AC-Out and is configured in AC-Out in VenusOS/Cerbo.
Could this be an issue with the “AS/NZS 4777.2:2020 stand alone app. M (no N-bypass)” grid code where exporting is not allowed?
John,
I reckon you are on to something, as can confirm testing with AS4777:2015 code the MP2 will export with ESS work well. So it is not my energy meter as originally thought.
Interesting… The reason I thought this might be the case was that the CEC website has only certified the MP2 for: “Stand - Alone Inverter With Grid Input - Battery Only”. Grid input being the operative words here…
So been doing some reading and from my understanding has to be “Multiple Mode Inverter” due to grid interaction not standalone.
Found the below flow chart which explain the difference.
This really defeats the purpose of having a MP2 with ESS on AC-In.
Maybe someone who knows this subject in more detail can assist.
Hi all,
Not sure if this topic is still active, but I’ve just purchased a MultiPlus-II 48/5000 and have been working through the setup with ESS and a grid meter.
I’ve noticed something curious regarding the AS/NZS 4777.2 standard:
  • With 4777.2:2020 Australia A and N-bypass enabled, the MultiPlus-II does not feed grid-side loads or back-feed from the battery.
  • However, with 4777.2:2015 and N-bypass enabled, everything works perfectly fine, including feeding grid-side loads.
I came across this updated inverter category and standards flow diagram from the Clean Energy Council:
Inverter categories and required standards relating to AS/NZS 4777.2:2020 Amd 2:2024
That document clarified some of the classification logic but didn’t explain why the MultiPlus-II can’t feed grid-side loads under the 2020 standard.
Does anyone have more insight into this limitation with the 2020 standard or know if there’s a workaround?
Thanks in advance.
Hi Jerome,
Unfortunately under 2020 standard if you want to use as ESS is not approved, I ended up disposing of my victron equipment and using a manufacture that wants to put the approvals through.
Disappointed as really enjoyed the victron quality but Australia market seems too small for them.
Hi Stuart Scott,
And out of curiosity, what brand did you go for? Might have to look to do the same. :frowning:
I have been having issues with the Multiplus II not exporting power when battery is connected
(if battery goes 100% it disconnects from grid if battery is under 100% it charges from grid )
and then the PV inverter sits their idle not exporting
so people are telling me to have the AC in and OUT out Neutrals bonded is this true for Australia
I could not find any wiring schematics showing this ?
however your saying its because of the 2020 standard ?
(I did try rolling the inverter back to 2015 but then it refused to grid connect at all )
I have been struggling with this as well. I was sold the Multiplus with CEC approval and advised that I can export to the Grid. And same as all of you I have wasted about 6 months on this on Grid Code 2020.
I have been emailing many Victron dealers including the one who sold me the equipment, and they just go silent when talking about the export.
I found a Victron dealer who was able to explain the CEC approval. Here is the answer I got.
Effectively, the Current MP-II 3 k -AU and 5 k -AU units, although listed, can be used only in these systems:
• Grid non-back feeding ESS systems.
• Grid-backup systems.
• Off-grid systems.
I find this extremely annoying that Victron would talk about in their youtube videos about Australia and Grid export… and then not get them approved to do so with the latest certification.
Completely defeats the purpose of ESS in my opinion.
I have all sorts of issues with the Grid code 2020
  • switching between inverter and grid mode would cause my PV inverter to reboot, On AC Out.
  • auto limiting of the inverter did not work properly mostly rebooted the inverter instead of rate limiting it.
  • Had a smart variable hot water controller would not work properly because it needed to see negative grid to ramp up. Hotwater was also on Non Essential so was costing money to heat.
  • Inverter would often auto switch from Grid to Inverter mode with no input.
  • I would see some infrequent random grid drops that I could not explain.
  • export attempts to the grid would completely drop the grid.
All of this has been solved with switching to 2015.
@MasterCATZ my system does not have the Neutral bypass, I thought for a long time this might have been the issue, with finding every person discussing no grid feedback had the exact same grid code as me at the time 2020 no n-bypass.
This article might help explain your questions, there is a Victron article which I can’t find right now, which from memory you bond the AC IN and AC Out Neutral, and have the MP 2 externally grounded (not through the switchboard/grid) Does Multiplus II disable Ground Relay automatically when Country/Grid code Australia AS/NZS4777.2:2015 (AC Neutral Path externally joined) is configured? - VictronEnergy