I am running a remote Microwave “tower”, no grid available - plain solar.
A few times a year I need generator support, typicaly in Winter in freezing tempertures.
So I need to have the generator warm up before the load comes on
Generator is of course connected to grid input
Is there a setting in the Multiplus that can delay grid usage for say 5 min after grid availabilty is detected?
@oskaratk you could install the CerboGx and use the rich features of the generator start and stop function. It has warm up and cool down times user selectable.
Multiplus units only have one input. Quattros have two inputs. The generator on input two doesn’t mean anything if the device is a Multiplus.
Do you have the latest CerboGX software? The generator cooldown and warmup provision are relatively late additions in the software. Update the CerboGX software to the latest version and those menus will be there.
Are you running an ESS system? I don’t think those provisions are available if the system is set up as ESS. Also, do you really have loads on the input and the output of your Multiplus? If you have no mains wouldn’t the loads only be on the output?
Without ESS and in a standard setup I think those provisions are included in the menu.
But upgrading the multi remotely - on a station that is in winter accessible by 2 - 3 hours hiking in steep terrain - that is pretty hot
Glad I have a multi as spare, so I can do a dry run