Multiplus II can a delay for charging be programmed when shore power connected?

Multiplus II 12/3000/120-50 2x120v

Is there a way to set a delay time (or a slow ramp rate) for the charger to start after input power is sensed?
I need to be able to give my generator time to warm up before the charger goes whole hog on charging.

Thank you

If you have a gx device in the system you could use the built in warmup timer, or use node red to create your own logic.

1 Like

I have a Cerbo GX to install… Looks like I will need to get after doing that sooner than I anticipated. Thank you.

How about the dynamic current limiter? You can configure that in VEconfigure and I’m assuming also VictronConnect. It’s been a while since I configured an inverter in VictronConnect so I can’t be sure. This is pretty much what the feature is meant for :slight_smile:

P.S. If you are using the generator start/stop feature of the Cerbo then I also recommend Derrick’s suggestion to the warmup timer.

That is a good point, I need to look at my programming again to see where I set it. With so much reading and learning sometimes I forget where I set a setting. I am using a 5500 Watt Onan, and the dynamic current limiter had an explanation/example using an inverter generator. There is a very good possibility that I have DCL turned off!

Thank you!

My Dynamic current limiter is enabled in the multiplus.:thinking: