Multiplus II 24/3000/70

good morning everyone, I have never noticed a behavior of the multiplus II and I would like to ask the community if it is natural. via the cerbo I set the multiplus state to OFF, but if I change the state to only charger, the output voltage also starts at 220v powering all the loads (I expected this if the setting had been ON). is everything normal?

Yes, that is normal.

What it will allow is your battery to remain charged and loads to be powered but in the even of a grid outage your battery will not be used.