Maximum grid power on dESS

Hi!
I have a limit of 4600 W of grid power contracted, if I go higher, I will be fined.

Do I have any chance to limit Grid Power to 4600, even if dESS is active?

Sometimes dESS starts to charge battery and brings grid consumption far over my limit.

I would like to have help from my MP even if SOC is below limit (15%) - there are only peaks sometimes where I’m going higher, but I would like to avoid in any case if possible, to go above my limit.

Thank you!

(MP2, pylontec)

On the CerboGx under settings → DESS the first setup panel called “System” has maximum import and maximum export power settings. Is that what you mean?

yes, but it doesn’t work…
Grid power is going far over this limit from time to time.

The parameters are not active limits. Neither for feed-in nor import. These are only parameters that are used to calculate the DESS schedule

You have to set a power limit directly in MP2

Thank you!

Is this the setting?
Do I have to check out Overruled by remote?