Unable to set the grid limit
My settings:
Grid: 220/230V + using Carlo Gavazzi as “Role: Grid”
Parallel config (2x Multi II 5000/48)
This Multiplus Cluster is working in the Mode=“On”
AC input 1: Grid
“Dynamic ESS” OFF
ESS: “Optimized without BatteryLife”
Battery SOC: 80% (actual status of 72% viewed in realtime)
“Grid current limit” set to 6A
ESS → “Grid setpoint” = 1000W
Grid feed-in → Limit system feed-in:ON & Maximum feed-in=1000W
My realtime Grid information shows: 4400W of consumption from Grid.
I cannot set the limit of my feed-in power. I have tried everything. Why is this happening???
I have had some issues, with the position of my Solar Inverter. If the location from your measurement(Carlo Gavazzi) is wrong, you automatically also get wrong info on your graphs. Could you provide some screenshots of your vrm?
Many Thanks for your fast answer, @larsh.
I have the Carlo Gavazzi in the grid input, far away from 2 (parallel) Multiplus II, about 15m away. I do not understand what does “wrong” in this case.
This issue was solved changed from ON to INVERTER and again to ON. But, I do not find a direct relation between the “Grid current limit” and the “MAX grid input power” concept. So, the only way to get 4600W max input power (tha max I can use from grid) is to setting a “Grid current limit” of 23A.
But in theory, 220Vx23A=5060W.
Sometimes I must change the “Grid current limit” to 40A to get max power of 4600W.
I have tried to use “Grid setpoint” and “Maximum feed-in” to could control the input MAX power and it has been imposible.
What am I doing wrong?
Many Thanks!!
Hi, I’m having the same issue, did you ever find a solution?
Edit: found it: Grid Current Limit with ESS Inverter Power Limit - #2 by fmckeogh