Hello community,
First, a bit about my setup. I have three MultiPlus II/48/8000 units, managed via a Cerbo GX. They are connected exclusively on the AC-IN side and are connected to my house network. On the DC side, six battery banks, each consisting of 16 EVE cells (around 96 kWh in total), are connected via Lynx Distributors and a Lynx Shunt.
The house network includes a Fronius Gen24 (which is also connected to the grid), two Symos, an Ohmpilot and a Wattpilot. The Cerbo GX is controlled via Modbus in mode 3. The Cerbo does not have its own AC-side energy meter. I wrote the energy management system myself. I control the Fronius BYD charging, Ohmpilot, Wattpilot and Victron systems every second. The system runs brilliantly, and since mid-July I have been almost completely self-sufficient.
On the Cerbo, I can see both the charging/discharging setpoint that I specify via Modbus, what is currently flowing from AC to DC or vice versa across the three phases, and the charging current measured by the Lynx. Until yesterday, this was always around 92%. In other words, when I had the Victrons charging at 10 kW, the DC charging power towards the batteries was around 9,200 W.
Yesterday, the Lynx Shunt failed (on the CAN side). I checked the wiring several times, etc., but nothing worked any more. The Cerbo could no longer detect the shunt. On the dealer’s advice, I then removed the small cables from the negative busbar at the bottom of the shunt; the LED went out. I then put everything back as it was, and the Cerbo detected the shunt again. However, the SOC and charging current were incorrect. The charging current was showing absurd values such as -20 kW. So I was told to switch off the MultiPlus units, after which the dealer calibrated the charging current.
The system is running again now… BUT: The previous 92% has now become around 50%! If I charge at 6 kW and the Cerbo also shows 3*2 kW on the AC-IN side, the Lynx Shunt shows less than 4 kW. Was the calibration carried out incorrectly? Nothing at all has changed in the DC wiring, MultiPlus units, etc.
The dealer has already provided a great deal of support. However, given the certainly unusual setup, it is understandably difficult for them to deal with this Lynx Shunt problem with yet more work free of charge as part of the usual warranty and support services. So I wanted to ask here before incurring additional costs elsewhere. Can anyone give me a tip?
How/when will the SOC calibrate itself again?