Lights flashing like a disco…

Oh boy, I moved my system and thought I had it all wired correctly and turned on the battery power switch to check and well….. nothing. All I have hooked up on the DC side is the batteries to the Lynx shunt/distributor, which goes to the inverter - on the AC side I have the generator/shore go through an automatic switch, then a surge guard, then to the Multiplus AC in, out through AC out 1 to the breaker panel….

So, I need help please… pretty please?! :grimacing:

This is indicate ( Hardware or EEPROM error)

These three LEDs will blink during programming of the assistants with VEConfigure3.
There is no error in that case.

In all other cases this indicates an error and the system will be off.
Typically occurs when firmware has been updated with an older version of VEFIash.
Can also occur during startup when data in the EEPROM (electrically erasable programmable read-only memory) is corrupted.
In some cases this can be solved by reprogramming in VEConfigure.
Solution
This indicates a configuration mismatch or hardware error.
There two methods to try (if it’s not a hardware error).

  1. Update firmware using VEFIash or VictronConnect
  2. If that doesn’t help, try the following:
    o Connect VEConfigure
    o Disable UPS (this is an example setting that will prompt for ‘Options for sending’ select ‘all settings’, and the unit will restart)
    o Write the all settings to the unit
    o Have the unit reset by VEConfigure
    o Select the UPS state again (or none if none was selected)
    o Rewrite all settings to the unit and let it reset.
1 Like