JK BMS + Multi RS Solar protocol issue
  • Jkong inverter BMS (latest firmware)
  • Victron Multi RS solar (latest firmware)
As I connect the battery to Multi RS via CAN (switch GX to the Can-bus BMS LV protocol) - all standard indicators like load, and PV disappear.
The battery’s SOC (State of Charge) shows correctly, but it doesn’t synchronize with the inverter and GX (the inverter maintains its own values - visible on the inverter’s display).
When I switch back to the Lynx Ion BMS protocol, the indicators return, but the connection with the Jk BMS disappears…
Using a type A cable (genuine Victron).
The problem, I think, lies in the fact that it connects via VeCan (unlike the Multiplus, which uses VeBus). And when you change the protocol, it starts to recognize the BMS but loses sight of everything else. I wonder if this can be resolved somehow?
It can be an underlying (temporary) problem with CAN ports on the Cerbo MK2, which is mentioned on this community in several places now.
Still, I will follow with interest this, because I already have a Multi RS Solar and I was thinking in getting a battery with JKBMS…
The issue is port speed.
The multi is 250kb/s and the bms is 500.
So you can’t have a daisy chain and have to set each port to a different speed, with terminations in both can busses.
You don’t make specific mention of what GX you have.
Using:
  • Setting CAN protocol to CAN-bus 500kbit:
I get to see the battery and MultiRS (PV charger):
You can let de JK BMS control the charge voltage limit (CVL), which is whar RCV (per cell) is in the JK BMS app:
(screenshot in next post because of limitation of this forum…)
JK BMS supports absorption/float voltage, Andy discusses them here: https://www.youtube.com/watch?v=eZX7CkEEq_8
Do not put the JK-BMS and the Multi-RS on the same CAN-Bus.
The Cerbo GX has 2 different CAN-bus, each have 2 RJ45 ports, so 4 ports in total.
Use one CAN-bus for the JK-BMS (on MK1 Cerbo’s, you must use the “BMS-CAN” bus for this).
Use the other CAN-bus to connect the Multi-RS.
Select different CAN protocols and speed for each bus.
Do not forget to add blue RJ-45 terminators to the 2 remaining CAN ports of the Cerbo, both CAN-bus must have a terminator on each end of their chain, so, in this case :
  • 2 on the cerbo
  • 1 on the Multi RS
  • 1 on the BMS … but it is already built-in inside the JK-BMS
Bonjour. . Je remonte le sujet.
J’ai installé mon système multiplus2 cerbo et batterie avec bms jk.
Mais je n’arrive pas a trouver le bms dans les paramètres victron.
Que faut il activer ou non pour réussir?
J’ai acheté le câble type A de victron, mais je ne vois rien
The settings will appear once the Cerbo detects the BMS. To do this, you need to connect the battery with a type-a cable to the BMS-can connector (CerboGX) - the battery will appear in Devices (in the Venus GUI interface).
Hi all,
I’m facing difficulty to have the communication between JK BMS and Cerbo GX MK2.
I tried with success with the Cerbo GX not MK2.
For the MK2 version, i placed the BMS on VE-CAN, Type A cable, put the baud rate com on CAN-bus BMS (500Kbits), Protocole Victron on the JK BMS, and I don’t see the BMS in the configuration. I tried to use the CAN termniator without any result.
Is anyone can explain my error on my stepup ?
Thanks a lot for your support
Kind regards,
Patrick.
Urgh, been struggling for ages to get my JK B Series BMS with the Comms board add-on working. Can’t believe it is just me forgetting to add the terminator on the Cerbo end. Thanks a lot for this!