Hub4control limits MaxDischargePower to ~51W regardless of load — Pylontech not discharging
System configuration:
· Cerbo GX, Venus OS v3.71
· 3x MultiPlus-II 48/3000/35-32
· 3x Pylontech US3000C (CAN, BMS-Can port, can1)
· 2x SmartSolar MPPT 250/60 (recently added, VE.Direct)
· Kostal Plenticore Plus on AC output (with BYD battery) — not registered as PV inverter in Victron
· ESS mode: Optimized without BatteryLife (Hub4Mode=2)
· DVCC enabled
Problem: Pylontech battery does not discharge even when grid consumption is present and SOC is at 100%. MaxDischargePower stays constantly at ~51-77W regardless of actual load. Switching on a 2000W load does not change MaxDischargePower. MultiPlus DC current shows 0A or negative (charging) while grid consumption is present.
History: System worked correctly for years without MPPT. Problem started after adding 2x MPPT and making changes in Node-RED. Node-RED is now completely disabled.
Diagnosis performed via SSH:
All ESS parameters are now correct after manual fixes:
BatteryLife/State: 9 (disabled)
BatteryLife/Flags: 0
BatteryLife/SocLimit: 11.0
BatteryLife/MinimumSocLimit: 11.0
BatteryLife/DischargedTime: 0
Hub4Mode: 2
AcPowerSetPoint: 30.0
MaxDischargePercentage: 1.0
MaxDischargePower (settings): -1.0 (unlimited)
MaxChargeCurrent (DVCC): 109A
Dc/0/Current (vebus): 0.0A
MaxDischargePower (hub4): ~51W (does not respond to load changes)
CAN connection: Previously had frequent BMS timeouts every 2-5 minutes caused by wrong DIP switch settings on master Pylontech module (DIP1 was OFF instead of ON). After fixing DIP1=ON on master module, CAN connection is now stable:
INF.can-bms: Manufacturer: ‘PYLON’
(no further timeouts)
hub4control log shows:
[Hub4Control] Using legacy BatteryInfo
Using active BMS: “com.victronenergy.battery.socketcan_can1”
Multi found “com.victronenergy.vebus.ttyS4”
[Hub4Control] Using regular BatteryInfo
What we already fixed (all were set incorrectly by old Node-RED flow):
· BatteryLife/State: was 10 (Recharge), now 9
· BatteryLife/Flags: was 3, now 0
· BatteryLife/SocLimit: was 70%, now 11%
· BatteryLife/MinimumSocLimit: was 19%, now 11%
· AcPowerSetPoint: was -90W, now +30W
· PvPowerSetpointOffset: was 200, now 0
· MaxDischargePercentage: was 1.9, now 1.0
· MaxChargeCurrent: was 1A, now 109A
· Pylontech DIP1: was OFF (slave mode), now ON (master mode)
Remaining problem: Despite all parameters being correct and CAN connection stable, MaxDischargePower remains at ~51W and does not respond to load changes. Even with a 2000W load active, the value stays at ~51W. The /Overrides/MaxDischargePower override is ignored or gets reset.
Question: Why does hub4control calculate MaxDischargePower at ~51W and ignore actual load? Could [Hub4Control] Using legacy BatteryInfo at startup cause incorrect internal calculations? Is there a way to reset hub4control’s internal state without reinstalling Venus OS?
Current dbus output:
/Settings/CGwacs/BatteryLife/State: 9
/Settings/CGwacs/BatteryLife/Flags: 0
/Settings/CGwacs/AcPowerSetPoint: 30.0
/hub4/MaxDischargePower: 51.0
/hub4/Overrides/MaxDischargePower: (gets reset)
/vebus.ttyS4/Dc/0/Current: 0.0
/system/Ac/Grid/L1/Power: 0.0
/system/Ac/Consumption/L1/Power: 111W
/battery.socketcan_can1/Soc: 100.0
/battery.socketcan_can1/Info/MaxDischargeCurrent: 111A
Here are some more infos:
root einstein:~# cat /var/log/hub4control/current
4000000069c7b2c1375e4b24 *** starting hub4control ***
4000000069c7b2c304dd6a2c hub4control v1.3.24 started
4000000069c7b2c304dd8584 Built with Qt 6.8.3 running on 6.8.3
4000000069c7b2c304dd8d54 Built on Mar 3 2026 at 14:11:31
4000000069c7b2c31063b39c Connecting to deprecated signal QDBusConnectionInterface::serviceOwnerChanged(QString,QString,QString)
4000000069c7b2c3150854ac Waiting for Hub-4/ESS assistant and localsettings
4000000069c7b2cd3b36b6dc Found localsettings
4000000069c7b2d703fe646c Found Hub-4/ESS assistant
4000000069c7b2df021b8ef4 Launching hub4control service
4000000069c7b2df0eaaf77c Registering service “com.victronenergy.hub4”
4000000069c7b2df154d29c4 [VeQItemDbusPublisher] Registered service “com.victronenergy.hub4”
4000000069c7b2df154f92f4 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7b2df15bb29ec No active BMS found
4000000069c7b2df15dfd88c [Hub4Control] Using legacy BatteryInfo
4000000069c7b2e00b7bcfcc [Hub4Control] Using legacy BatteryInfo
4000000069c7b2e01187443c Grid meter found “com.victronenergy.grid.cg_76662731”
4000000069c7b2e012b99e04 Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7b2e239490bf4 Multi found “com.victronenergy.vebus.ttyS4”
4000000069c7b2e300d7f71c [Hub4Control] Using regular BatteryInfo
4000000069c7b8022074672c Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7b8022074a1c4 No active BMS found
4000000069c7b80227cba904 No active BMS found
4000000069c7b8082dfcf10c Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7b8082dffd354 No active BMS found
4000000069c7b80905668f8c Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7b80d2ee2ec0c Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7b80d2ee30b4c No active BMS found
4000000069c7b80d36d6fe6c No active BMS found
4000000069c7b8100436a2dc Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7b8100436c604 No active BMS found
4000000069c7b8103555965c Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7ba150302d5fc Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7ba150305bc2c No active BMS found
4000000069c7ba15098216f4 No active BMS found
4000000069c7ba240ee65a9c Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7ba240ee679dc No active BMS found
4000000069c7ba2426ee2dcc Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7ba381587cd7c Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7ba381587f0a4 No active BMS found
4000000069c7ba381af9b93c No active BMS found
4000000069c7ba422a3d2604 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7ba422a3d492c No active BMS found
4000000069c7ba43111cda0c Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7c19a29d0009c Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7c19a29d01fdc No active BMS found
4000000069c7c19a304454b4 No active BMS found
4000000069c7c2d4274ae42c Grid meter “com.victronenergy.grid.cg_76662731” disappeared.
4000000069c7c32525deec64 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7c32525df0ba4 No active BMS found
4000000069c7c32605df325c Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7c32e2a8ac134 Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7c32e2a921434 No active BMS found
4000000069c7c32e2fbff214 No active BMS found
4000000069c7c33628be36c4 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7c33628be5604 No active BMS found
4000000069c7c33707dddcd4 Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7c3462623a23c Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7c3462623c17c No active BMS found
4000000069c7c3462c6f05dc No active BMS found
4000000069c7c34e015f66fc Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7c34e01c940a4 No active BMS found
4000000069c7c34e17115b7c Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7c3600661db94 Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7c3600661fad4 No active BMS found
4000000069c7c3600dca0974 No active BMS found
4000000069c7c3650e66d9fc Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7c3650e6927d4 No active BMS found
4000000069c7c3653633e09c Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7c41512619ac4 Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7c4151261bdec No active BMS found
4000000069c7c41517f82584 No active BMS found
4000000069c7c419286437b4 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7c419286456f4 No active BMS found
4000000069c7c41a101eee24 Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7c56b31285bb4 Grid meter found “com.victronenergy.grid.cg_76662731”
4000000069c7cb190b203a7c Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7cb190b2059bc No active BMS found
4000000069c7cb19124033fc No active BMS found
4000000069c7cb1a1a8e4954 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7cb1a1a8e6894 No active BMS found
4000000069c7cb1a32f03ebc Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7cc0d1a42678c Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7cc0d1a428ab4 No active BMS found
4000000069c7cc0d1e93fae4 No active BMS found
4000000069c7cc470274e224 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7cc470275054c No active BMS found
4000000069c7cc4715aaedac Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7d61102d56cfc *** Venus OS v3.71 booted (0) ***
4000000069c7d611238cfd84 *** starting hub4control ***
4000000069c7d6120f7a93ec hub4control v1.3.24 started
4000000069c7d6120f7ab32c Built with Qt 6.8.3 running on 6.8.3
4000000069c7d6120f7abafc Built on Mar 3 2026 at 14:11:31
4000000069c7d6121a4fc954 Connecting to deprecated signal QDBusConnectionInterface::serviceOwnerChanged(QString,QString,QString)
4000000069c7d6121ab1dacc Waiting for Hub-4/ESS assistant and localsettings
4000000069c7d61e239b8444 Found localsettings
4000000069c7d6272b57d91c Found Hub-4/ESS assistant
4000000069c7d62f2a2aea0c Launching hub4control service
4000000069c7d62f2f543fc4 Registering service “com.victronenergy.hub4”
4000000069c7d62f316fe434 [VeQItemDbusPublisher] Registered service “com.victronenergy.hub4”
4000000069c7d62f3170075c Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7d62f32a87f8c No active BMS found
4000000069c7d62f32b66624 Grid meter found “com.victronenergy.grid.cg_76662731”
4000000069c7d62f35b66b6c [Hub4Control] Using legacy BatteryInfo
4000000069c7d6303990ee4c [Hub4Control] Using legacy BatteryInfo
4000000069c7d63039f93d6c Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7d63235e92b9c Multi found “com.victronenergy.vebus.ttyS4”
4000000069c7d6330641fb6c [Hub4Control] Using regular BatteryInfo
4000000069c7f0de2e4db8bc Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7f0de2e4ddbe4 No active BMS found
4000000069c7f0de35e3e40c No active BMS found
4000000069c7f0f136b539e4 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7f0f136b83f54 No active BMS found
4000000069c7f0f21100ca74 Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7f2f02f8342ec Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7f2f02f83622c No active BMS found
4000000069c7f2f0338f2e3c No active BMS found
4000000069c7f2f622f87614 Battery found “com.victronenergy.battery.socketcan_can0”
4000000069c7f2f62379b7ec No active BMS found
4000000069c7f2f634d1f70c Using active BMS: “com.victronenergy.battery.socketcan_can0”
4000000069c7f6122f2bd034 Battery “com.victronenergy.battery.socketcan_can0” disappeared.
4000000069c7f6122f2bef74 No active BMS found
4000000069c7f61234e1411c No active BMS found
4000000069c7f61516f73bfc Battery found “com.victronenergy.battery.socketcan_can0”
4000000069c7f61516f75b3c No active BMS found
4000000069c7f61528f8460c Using active BMS: “com.victronenergy.battery.socketcan_can0”
4000000069c7f7b73670d22c Battery “com.victronenergy.battery.socketcan_can0” disappeared.
4000000069c7f7b73673c414 No active BMS found
4000000069c7f7b80041b644 No active BMS found
4000000069c7f7c90dff7d0c Battery found “com.victronenergy.battery.socketcan_can0”
4000000069c7f7c90dff9c4c No active BMS found
4000000069c7f7c9210d5f54 Using active BMS: “com.victronenergy.battery.socketcan_can0”
4000000069c7f7d20b499084 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7f7d20b4d16dc Using active BMS: “com.victronenergy.battery.socketcan_can0”
4000000069c7f7d22178bbb4 Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7f7d3370741e4 Battery “com.victronenergy.battery.socketcan_can0” disappeared.
4000000069c7f7d337076124 Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7f7d4044813b4 No active BMS found
4000000069c7f7f137507044 Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7f7f137508f84 No active BMS found
4000000069c7f7fc0a7b47ec Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7f7fc0a8bbadc No active BMS found
4000000069c7f7fc1c154714 Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c7f8010ac312d4 Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c7f8010ac33214 No active BMS found
4000000069c7f80113722834 No active BMS found
4000000069c7f8043654ab24 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c7f8043654ce4c No active BMS found
4000000069c7f80513c3c6bc Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c809312cb99f84 Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c809312cbc9554 No active BMS found
4000000069c8093131f74474 No active BMS found
4000000069c80944263cc3d4 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c80944263cdf2c No active BMS found
4000000069c80944366145b4 Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c8095b2851e834 Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c8095b28520774 No active BMS found
4000000069c8095b2d2b6484 No active BMS found
4000000069c8096029447dc4 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c809602944991c No active BMS found
4000000069c809610360d864 Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c80df9257ae304 Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c80df925a12014 No active BMS found
4000000069c80df92a1e2484 No active BMS found
4000000069c80e240e46de7c Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c80e240e49bcdc No active BMS found
4000000069c80e2429412264 Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c80edd2f730a94 Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c80edd2f760834 No active BMS found
4000000069c80edd342914ac No active BMS found
4000000069c80f6501af1d3c Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c80f6501b20b3c No active BMS found
4000000069c80f6521254c54 Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c80f9d04baaf8c Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c80f9d04bd99a4 No active BMS found
4000000069c80f9d0b7426dc No active BMS found
4000000069c80fa721a8728c Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c80fa721a895b4 No active BMS found
4000000069c80fa735fc2ae4 Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c80fd222bd1ac4 Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c80fd222c02034 No active BMS found
4000000069c80fd2276bb684 No active BMS found
4000000069c8106e2731032c Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c8106e2731226c No active BMS found
4000000069c8106f0b420ea4 Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c8f18204c419b4 *** Venus OS v3.71 booted (0) ***
4000000069c8f183151e075c *** starting hub4control ***
4000000069c8f1841521d404 hub4control v1.3.24 started
4000000069c8f1841521ef5c Built with Qt 6.8.3 running on 6.8.3
4000000069c8f1841521fb14 Built on Mar 3 2026 at 14:11:31
4000000069c8f18423e49f1c Connecting to deprecated signal QDBusConnectionInterface::serviceOwnerChanged(QString,QString,QString)
4000000069c8f184272965f4 Waiting for Hub-4/ESS assistant and localsettings
4000000069c8f1900ed101c4 Found localsettings
4000000069c8f19925fa7b14 Found Hub-4/ESS assistant
4000000069c8f1a1096cba34 Launching hub4control service
4000000069c8f1a10f8d2da4 Registering service “com.victronenergy.hub4”
4000000069c8f1a11739a7e4 [VeQItemDbusPublisher] Registered service “com.victronenergy.hub4”
4000000069c8f1a11739cb0c Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c8f1a117beae94 No active BMS found
4000000069c8f1a118f6c134 Grid meter found “com.victronenergy.grid.cg_76662731”
4000000069c8f1a11acb98a4 [Hub4Control] Using legacy BatteryInfo
4000000069c8f1a328445b74 [Hub4Control] Using legacy BatteryInfo
4000000069c8f1a32df6615c Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069c8f1a6057f14e4 Multi found “com.victronenergy.vebus.ttyS4”
4000000069c8f1a60d267e44 [Hub4Control] Using regular BatteryInfo
4000000069c8f55f32cf6c64 Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069c8f55f32cf8f8c No active BMS found
4000000069c8f55f38eb76ec No active BMS found
4000000069c8f56927716b74 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069c8f5692771966c No active BMS found
4000000069c8f5693b7fdd6c Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069cba2bd1f6b76f4 Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069cba2bd1f6bb574 No active BMS found
4000000069cba2bd27b4c5a4 No active BMS found
4000000069cba67705277734 *** Venus OS v3.71 booted (0) ***
4000000069cba67818d87f1c *** starting hub4control ***
4000000069cba6792826c154 hub4control v1.3.24 started
4000000069cba6792826e094 Built with Qt 6.8.3 running on 6.8.3
4000000069cba6792826ec4c Built on Mar 3 2026 at 14:11:31
4000000069cba67932f981d4 Connecting to deprecated signal QDBusConnectionInterface::serviceOwnerChanged(QString,QString,QString)
4000000069cba67935d27b04 Waiting for Hub-4/ESS assistant and localsettings
4000000069cba6843a2af014 Found localsettings
4000000069cba68e2c19a27c Found Hub-4/ESS assistant
4000000069cba698182655bc Launching hub4control service
4000000069cba6982128460c Registering service “com.victronenergy.hub4”
4000000069cba698253ec464 [VeQItemDbusPublisher] Registered service “com.victronenergy.hub4”
4000000069cba698253ee78c Battery found “com.victronenergy.battery.socketcan_can1”
4000000069cba6982622a06c No active BMS found
4000000069cba6982622bbc4 Grid meter found “com.victronenergy.grid.cg_76662731”
4000000069cba698283dcfac [Hub4Control] Using legacy BatteryInfo
4000000069cba69a35dadb8c [Hub4Control] Using legacy BatteryInfo
4000000069cba69a3993b53c Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069cba69f1366c624 Multi found “com.victronenergy.vebus.ttyS4”
4000000069cba69f1c1a252c [Hub4Control] Using regular BatteryInfo
4000000069cba80505d9fe54 *** Venus OS v3.71 booted (0) ***
4000000069cba8051a11ddc4 *** starting hub4control ***
4000000069cba8061dbabd9c hub4control v1.3.24 started
4000000069cba8061dc29d3c Built with Qt 6.8.3 running on 6.8.3
4000000069cba8061dd5cf4c Built on Mar 3 2026 at 14:11:31
4000000069cba80621050e6c Connecting to deprecated signal QDBusConnectionInterface::serviceOwnerChanged(QString,QString,QString)
4000000069cba80622d1fa84 Waiting for Hub-4/ESS assistant and localsettings
4000000069cba8113a89c954 Found localsettings
4000000069cba81b21c0c134 Found Hub-4/ESS assistant
4000000069cba8232a10bed4 Launching hub4control service
4000000069cba823389d62a4 Registering service “com.victronenergy.hub4”
4000000069cba82401efa8ac [VeQItemDbusPublisher] Registered service “com.victronenergy.hub4”
4000000069cba82401efcbd4 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069cba82402b93654 No active BMS found
4000000069cba82402e21344 Grid meter found “com.victronenergy.grid.cg_76662731”
4000000069cba8240614a9dc [Hub4Control] Using legacy BatteryInfo
4000000069cba82730830b64 [Hub4Control] Using legacy BatteryInfo
4000000069cba82738fbab5c Using active BMS: “com.victronenergy.battery.socketcan_can1”
4000000069cba82b0d3825cc Multi found “com.victronenergy.vebus.ttyS4”
4000000069cba82b13330fdc [Hub4Control] Using regular BatteryInfo
4000000069cbb6621ce481dc Battery “com.victronenergy.battery.socketcan_can1” disappeared.
4000000069cbb6621ce78b34 No active BMS found
4000000069cbb662240d1e4c No active BMS found
4000000069cbb67026d05914 Battery found “com.victronenergy.battery.socketcan_can1”
4000000069cbb67026d907bc No active BMS found
4000000069cbb6710132e474 Using active BMS: “com.victronenergy.battery.socketcan_can1”
root einstein:~# cat /var/log/can-bus-bms.can1/current
4000000069cba6420de82864 Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba6420de847a4 The following gateways were found:
4000000069cba6420de84f74 --------------------------------------------------------------
4000000069cba6420de85b2c socketcan:can0 can0
4000000069cba6420de862fc --------------------------------------------------------------
4000000069cba6420de86acc INF.task: done in 000.002
4000000069cba6430cf07a24 *** starting can-bus-bms ***
4000000069cba6430e88c97c can-bus-bms v0.71
4000000069cba6430ea2c1ec
4000000069cba6430ea2dd44 -------- dumping backlog -------
4000000069cba6430ea2e514 INF.canhw_drv: adding driver socketcan
4000000069cba6430ea2ece4 INF.skcan: ignoring can1, interface is not up
4000000069cba6430ea2f89c ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba6430ea6d0fc Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba6430ea6e09c The following gateways were found:
4000000069cba6430ea6e86c --------------------------------------------------------------
4000000069cba6430ea6f424 socketcan:can0 can0
4000000069cba6430ea6f80c --------------------------------------------------------------
4000000069cba6430ea703c4 INF.task: done in 000.002
4000000069cba6440e307fec *** starting can-bus-bms ***
4000000069cba6440fba5c0c can-bus-bms v0.71
4000000069cba6440fd3db64
4000000069cba6440fd3f6bc -------- dumping backlog -------
4000000069cba6440fd3fe8c INF.canhw_drv: adding driver socketcan
4000000069cba6440fd4065c INF.skcan: ignoring can1, interface is not up
4000000069cba6440fd40e2c ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba6440fdafb9c Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba6440fdb0f24 The following gateways were found:
4000000069cba6440fdb1adc --------------------------------------------------------------
4000000069cba6440fdb22ac socketcan:can0 can0
4000000069cba6440fdb2a7c --------------------------------------------------------------
4000000069cba6440fdb324c INF.task: done in 000.002
4000000069cba6450fa83b6c *** starting can-bus-bms ***
4000000069cba645114b15fc can-bus-bms v0.71
4000000069cba6451168043c
4000000069cba64511682b4c -------- dumping backlog -------
4000000069cba6451168331c INF.canhw_drv: adding driver socketcan
4000000069cba64511683ed4 INF.skcan: ignoring can1, interface is not up
4000000069cba645116846a4 ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba645116d8664 Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba645116da1bc The following gateways were found:
4000000069cba645116da98c --------------------------------------------------------------
4000000069cba645116db544 socketcan:can0 can0
4000000069cba645116db92c --------------------------------------------------------------
4000000069cba645116dc4e4 INF.task: done in 000.002
4000000069cba64610ee7324 *** starting can-bus-bms ***
4000000069cba646129fd08c can-bus-bms v0.71
4000000069cba64612c4b9c4
4000000069cba64612c4d134 -------- dumping backlog -------
4000000069cba64612c4d904 INF.canhw_drv: adding driver socketcan
4000000069cba64612c4e0d4 INF.skcan: ignoring can1, interface is not up
4000000069cba64612c4e8a4 ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba64612cc5ecc Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba64612cc763c The following gateways were found:
4000000069cba64612cc7e0c --------------------------------------------------------------
4000000069cba64612cc85dc socketcan:can0 can0
4000000069cba64612cc8dac --------------------------------------------------------------
4000000069cba64612cc957c INF.task: done in 000.003
4000000069cba647124f6a84 *** starting can-bus-bms ***
4000000069cba64713f398ec can-bus-bms v0.71
4000000069cba6471405ffdc
4000000069cba64714061364 -------- dumping backlog -------
4000000069cba64714061b34 INF.canhw_drv: adding driver socketcan
4000000069cba64714062304 INF.skcan: ignoring can1, interface is not up
4000000069cba64714062ebc ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba6471408807c Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba6471408901c The following gateways were found:
4000000069cba647140897ec --------------------------------------------------------------
4000000069cba6471408a3a4 socketcan:can0 can0
4000000069cba6471408ab74 --------------------------------------------------------------
4000000069cba6471408b344 INF.task: done in 000.002
4000000069cba64813906664 *** starting can-bus-bms ***
4000000069cba64815b7612c can-bus-bms v0.71
4000000069cba648160565d4
4000000069cba64816058514 -------- dumping backlog -------
4000000069cba64816058ce4 INF.canhw_drv: adding driver socketcan
4000000069cba648160594b4 INF.skcan: ignoring can1, interface is not up
4000000069cba64816059c84 ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba648160a3c1c Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba648160a538c The following gateways were found:
4000000069cba648160a5b5c --------------------------------------------------------------
4000000069cba648160a632c socketcan:can0 can0
4000000069cba648160a6afc --------------------------------------------------------------
4000000069cba648160a76b4 INF.task: done in 000.007
4000000069cba6491555d484 *** starting can-bus-bms ***
4000000069cba64917349aec can-bus-bms v0.71
4000000069cba649174bff34
4000000069cba649174c1a8c -------- dumping backlog -------
4000000069cba649174c225c INF.canhw_drv: adding driver socketcan
4000000069cba649174c2a2c INF.skcan: ignoring can1, interface is not up
4000000069cba649174c31fc ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba649175073d4 Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba64917508b44 The following gateways were found:
4000000069cba64917509314 --------------------------------------------------------------
4000000069cba64917509ae4 socketcan:can0 can0
4000000069cba6491750a2b4 --------------------------------------------------------------
4000000069cba6491750ae6c INF.task: done in 000.002
4000000069cba64a168a0ec4 *** starting can-bus-bms ***
4000000069cba64a17fc4fec can-bus-bms v0.71
4000000069cba64a181375b4
4000000069cba64a1813910c -------- dumping backlog -------
4000000069cba64a181398dc INF.canhw_drv: adding driver socketcan
4000000069cba64a1813a0ac INF.skcan: ignoring can1, interface is not up
4000000069cba64a1813a87c ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba64a181aad5c Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba64a181ac4cc The following gateways were found:
4000000069cba64a181acc9c --------------------------------------------------------------
4000000069cba64a181ad854 socketcan:can0 can0
4000000069cba64a181ae024 --------------------------------------------------------------
4000000069cba64a181ae7f4 INF.task: done in 000.002
4000000069cba64b17c768f4 *** starting can-bus-bms ***
4000000069cba64b196a476c can-bus-bms v0.71
4000000069cba64b1981bb54
4000000069cba64b1981d6ac -------- dumping backlog -------
4000000069cba64b1981de7c INF.canhw_drv: adding driver socketcan
4000000069cba64b1981e64c INF.skcan: ignoring can1, interface is not up
4000000069cba64b1981ee1c ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba64b19900b64 Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba64b19902aa4 The following gateways were found:
4000000069cba64b19903274 --------------------------------------------------------------
4000000069cba64b199045fc socketcan:can0 can0
4000000069cba64b19904dcc --------------------------------------------------------------
4000000069cba64b19905984 INF.task: done in 000.002
4000000069cba64c1a7be264 *** starting can-bus-bms ***
4000000069cba64c1bc225d4 can-bus-bms v0.71
4000000069cba64c1bdeba3c
4000000069cba64c1bded594 -------- dumping backlog -------
4000000069cba64c1bdedd64 INF.canhw_drv: adding driver socketcan
4000000069cba64c1bdee534 INF.skcan: ignoring can1, interface is not up
4000000069cba64c1bdeed04 ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba64c1be4e45c Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba64c1be4fbcc The following gateways were found:
4000000069cba64c1be4ffb4 --------------------------------------------------------------
4000000069cba64c1be50b6c socketcan:can0 can0
4000000069cba64c1be5133c --------------------------------------------------------------
4000000069cba64c1be51b0c INF.task: done in 000.002
4000000069cba64d1d09f7b4 *** starting can-bus-bms ***
4000000069cba64d1f875f7c can-bus-bms v0.71
4000000069cba64d1fb2383c
4000000069cba64d1fb25394 -------- dumping backlog -------
4000000069cba64d1fb25b64 INF.canhw_drv: adding driver socketcan
4000000069cba64d1fb26334 INF.skcan: ignoring can1, interface is not up
4000000069cba64d1fb26eec ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba64d1fc5eb34 Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba64d1fc60e5c The following gateways were found:
4000000069cba64d1fc6162c --------------------------------------------------------------
4000000069cba64d1fc621e4 socketcan:can0 can0
4000000069cba64d1fc629b4 --------------------------------------------------------------
4000000069cba64d1fc63184 INF.task: done in 000.004
4000000069cba64e1c12dde4 *** starting can-bus-bms ***
4000000069cba64e1db57ddc can-bus-bms v0.71
4000000069cba64e1dd10c8c
4000000069cba64e1dd127e4 -------- dumping backlog -------
4000000069cba64e1dd1339c INF.canhw_drv: adding driver socketcan
4000000069cba64e1dd13b6c INF.skcan: ignoring can1, interface is not up
4000000069cba64e1dd1433c ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba64e1dd440dc Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba64e1dd4507c The following gateways were found:
4000000069cba64e1dd4584c --------------------------------------------------------------
4000000069cba64e1dd46404 socketcan:can0 can0
4000000069cba64e1dd467ec --------------------------------------------------------------
4000000069cba64e1dd473a4 INF.task: done in 000.002
4000000069cba64f1d541844 *** starting can-bus-bms ***
4000000069cba64f1ef99a84 can-bus-bms v0.71
4000000069cba64f1f11357c
4000000069cba64f1f1150d4 -------- dumping backlog -------
4000000069cba64f1f1158a4 INF.canhw_drv: adding driver socketcan
4000000069cba64f1f116074 INF.skcan: ignoring can1, interface is not up
4000000069cba64f1f116844 ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba64f1f1490dc Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba64f1f14a07c The following gateways were found:
4000000069cba64f1f14a84c --------------------------------------------------------------
4000000069cba64f1f14b404 socketcan:can0 can0
4000000069cba64f1f14bbd4 --------------------------------------------------------------
4000000069cba64f1f14c3a4 INF.task: done in 000.002
4000000069cba6501eb05c84 *** starting can-bus-bms ***
4000000069cba65021352ebc can-bus-bms v0.71
4000000069cba650214d238c
4000000069cba650214d3ee4 -------- dumping backlog -------
4000000069cba650214d46b4 INF.canhw_drv: adding driver socketcan
4000000069cba650214d4e84 INF.skcan: ignoring can1, interface is not up
4000000069cba650214d5654 ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba6502150b1b4 Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba6502150c53c The following gateways were found:
4000000069cba6502150cd0c --------------------------------------------------------------
4000000069cba6502150d8c4 socketcan:can0 can0
4000000069cba6502150dcac --------------------------------------------------------------
4000000069cba6502150e864 INF.task: done in 000.002
4000000069cba65120c32b3c *** starting can-bus-bms ***
4000000069cba651258dee04 can-bus-bms v0.71
4000000069cba65126884fac
4000000069cba65126886eec -------- dumping backlog -------
4000000069cba651268876bc INF.canhw_drv: adding driver socketcan
4000000069cba65126888274 INF.skcan: ignoring can1, interface is not up
4000000069cba65126888a44 ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba65126889214 Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba65126889dcc The following gateways were found:
4000000069cba6512688a59c --------------------------------------------------------------
4000000069cba651268bbe94 socketcan:can0 can0
4000000069cba651268bca4c --------------------------------------------------------------
4000000069cba651268bd604 INF.task: done in 000.021
4000000069cba65222015474 *** starting can-bus-bms ***
4000000069cba65225770aa4 can-bus-bms v0.71
4000000069cba652258fe204
4000000069cba652258ff974 -------- dumping backlog -------
4000000069cba6522590052c INF.canhw_drv: adding driver socketcan
4000000069cba65225900914 INF.skcan: ignoring can1, interface is not up
4000000069cba652259014cc ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba652259350ec Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba65225936474 The following gateways were found:
4000000069cba6522593685c --------------------------------------------------------------
4000000069cba65225937414 socketcan:can0 can0
4000000069cba65225937be4 --------------------------------------------------------------
4000000069cba652259383b4 INF.task: done in 000.002
4000000069cba65323be332c *** starting can-bus-bms ***
4000000069cba653268a7a5c can-bus-bms v0.71
4000000069cba653269d6234
4000000069cba653269d79a4 -------- dumping backlog -------
4000000069cba653269d855c INF.canhw_drv: adding driver socketcan
4000000069cba653269d8944 INF.skcan: ignoring can1, interface is not up
4000000069cba653269d94fc ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba653269ea66c Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba653269eb60c The following gateways were found:
4000000069cba653269ebddc --------------------------------------------------------------
4000000069cba653269ec994 socketcan:can0 can0
4000000069cba653269ed164 --------------------------------------------------------------
4000000069cba653269ee4ec INF.task: done in 000.001
4000000069cba65424af55a4 *** starting can-bus-bms ***
4000000069cba6542779c42c can-bus-bms v0.71
4000000069cba65427905d54
4000000069cba654279078ac -------- dumping backlog -------
4000000069cba6542790807c INF.canhw_drv: adding driver socketcan
4000000069cba6542790884c INF.skcan: ignoring can1, interface is not up
4000000069cba6542790901c ERR.canhw_drv: Could not find gateway ‘socketcan:can1’
4000000069cba65427933bb4 Specified CAN-bus gateway ‘socketcan:can1’ not found!
4000000069cba65427934b54 The following gateways were found:
4000000069cba65427935324 --------------------------------------------------------------
4000000069cba65427935edc socketcan:can0 can0
4000000069cba654279362c4 --------------------------------------------------------------
4000000069cba65427936e7c INF.task: done in 000.001
4000000069cba67634a378b4 *** Venus OS v3.71 booted (0) ***
4000000069cba68811da80d4 *** starting can-bus-bms ***
4000000069cba6881bf8166c can-bus-bms v0.71
4000000069cba804351345cc *** Venus OS v3.71 booted (0) ***
4000000069cba81606f4ff8c *** starting can-bus-bms ***
4000000069cba8160aee1e5c can-bus-bms v0.71
4000000069cbb6621bc6cd3c
4000000069cbb6621bc6e4ac -------- dumping backlog -------
4000000069cbb6621bc6f064 INF.canhw_drv: adding driver socketcan
4000000069cbb6621bc6f834 INF.: Using can1
4000000069cbb6621bc6fc1c INF.can-bms: Product ID from settings: B009
4000000069cbb6621bc703ec INF.can-bms: dbus_service: registering name com.victronenergy.battery.socketcan_can1
4000000069cbb6621bc7138c INF.can-bms: Manufacturer: ‘PYLON’
4000000069cbb6621bc71b5c ERR.bms: bms timeout
4000000069cbb6621bc71f44 INF.can-bms: disconnecting from dbus
4000000069cbb67026237f14 INF.can-bms: dbus_service: registering name com.victronenergy.battery.socketcan_can1
4000000069cbb6702684cd3c INF.can-bms: Manufacturer: ‘PYLON’
I hope, you see my problem with all the info?!
I am lost and AI support as well :slight_smile:
Thanks Thomas
Das Problem wurde gelöst. Es war der Lade- und Entladestrom auf 1% des Maximalstroms gestellt, was man in der klassischen Console nicht sehen konnte, in der neuen hingegen schon. Nun funktioniert wieder alles.