Gui-v2 is showing grid as disconnected while its not

As long as my Multiplus II 3 Phase system is on the Grid is shown nearly “correctly”. Since all my load is on the input side I would expect the AC Loads and my EVCS shown between Grid and Inverter

With Node Red I switch my Multiplus II to off, when my battery is on minimum SOC, my MPPT do not delivery enough solar and the Multiplus should not charge. This should minimize the standby power lose since I do not need the Multiplus when they should not charge or invert power.
Then GUI-V2 shows my grid as disconnected which is not correct. And the data from my EM24 gridmeter is not shown on the Grid part.

In VRM the details (Phase 1-3) from Grid are lost and are not shown

In GUI V1 everything is shown correctly. Including the single phase use.

Hi @Nicolai , thank you for the report, we’ll look into this

2 Likes

Hi @Nicolai , can you try with the v3.52~2 beta that is out per just now and let me know if that fixes this?

1 Like

@mpvader I have now updated v3.52~2
As soon as the Multiplus II are switched of the VRM loses the phase details for the grid phases

In Gui V2 the Grid details for the 3Phase are now shown.

1 Like

Perfect! From a gui-v2 point of view at least.

I’ve made a note to get vrm checked as well.

Thank you for the quick feedback.

1 Like