Hi,
I have a MultiPlus II GX 48/5000 set up in ESS mode with a 16 kWh LFP battery and a VM-3P75CT in a three-phase system.

To avoid wasting power when the battery is empty, I found that I can power off the MultiPlus using Modbus register 33 (1 = Charger Only; 2 = Inverter Only; 3 = On; 4 = Off) — by setting it to 4, and then back to 3 when excess solar power is detected.
I’ve created two Home Assistant automations to handle these actions.

The only problem I’ve found is this:
When I switch the MultiPlus back on, feed-in doesn’t work until the ESS relay test is performed. The issue is that the relay test only runs if the battery voltage rises above 56 V (which corresponds to 100 % SOC for an LFP battery), or when the reported battery SOC increases above 20 %.

Is there any way to overcome this behavior?
It seems that these thresholds are hardcoded, which isn’t very flexible for a charger/inverter meant to work with different battery setups and chemistries.
Is there maybe a way to manually trigger the ESS relay test?

Can you change the mode in the GUI

Thanks, but this doesn’t solve the ESS relay test delayed until the SOC rise above 20%.

I try to understand what your problem is.(I do not recognize this problem)

What is the value in ESS “Minimum SOC (unless grid fails)“

Update:
After upgrading the MultiPlus II firmware from 557 → 558 and the ESS assistant from 018C → 018E, the issue disappeared.
Now, when the MultiPlus II is re-enabled (Modbus register 33 from 4 → 3), the ESS relay test is immediately marked as “completed”, even when the battery is below 20 % SOC.