Hello,
I have a problem with essential loads (AC Out1) dropping off on mains failure. After looking through all settings, I can’t find anything wrong, hence I decided to post the question here while awaiting visit from electricians that installed and commissioned the system (I may be waiting some time for that).
My setup consist of the following components:
- MultiPlus-II 48/8000/110-100
- 3x Pylontech US3000C
- MPPT RS 450/200 (with 8.8kWp connected in E-W configuration)
- External grid meter (measuring directly after main house breaker and connected by modbus to Cerbo)
- Cerbo GX
The installation location is Spain, the MultiPlus is configured to use Spanish grid code. The system is configured as ESS and works for just over a year now, and it works well - using solar to charge batteries, feed loads, export, import when needed to support load and/or charge batteries if requested - all as expected.
However when the system was commissioned, the essential loads output was brought back to my main electrical board, terminated on the breaker and left unused (re-wiring the board was not in scope in the installation).
I finally decided to make use of it, with notification of upcoming 1/2 day power disruption in my area being a good motivator. I now have all loads separated nicely - 2 RCDs with everything I consider essential connected to critical load (AC Out1) and all heavy loads (heat pumps, water heating, oven etc) remaining unprotected - these loads are connected before MultiPlus, on AC In, AC Out2 is unused.
As far as Cerbo screen and VRM reports, it all looks good - the ‘precious’ part of my load now shows as ‘Essential Loads’ and reminder as ‘AC Loads’.
Here is where everything good ends and comes the problem and the question. After re-connecting the power and giving MultiPlus few minutes to synchronise with the grid and return to normal operation, with battery charged to c. 60%, I pulled the main incoming breaker down hoping the house remains powered. I got disappointed as everything dropped offline. I was so puzzled that I pulled the breaker back up without checking the status of the MultiPlus, but I can obviously do it again if that’s of any use.
I had another 2 short power disruptions since (caused by grid issues) and on both occasions the same happened. First time I wasn’t home and the second time the interruption was few seconds long, so I didn’t manage to get to the inverter in time, but I was watching the screen showing only unprotected loads supplied until the magic relay clicked few minutes later to bring the lights back.
Summarising, what I achieved now is that my house remains dark 5 mins longer than the entire neighbourhood as it takes so long for Essential Loads to re-connect after the power is back.
While I am not confident I have been through all posts reporting similar problem, I did fair bit of searching and I found nothing that would help me resolve the problem.
Is there anything someone here can suggest I should check, try or test?
While I am not certified electrician, I have background in electronics and telecoms, so I have good understanding of electrical basics. I also have the MK3 cable, so I can download/check the config from MultiPlus.
Thank you in advance.
Regards,
Sergiusz