As an additional information, this happens when the water heater is on. If I use air conditioning, the charging current stabilized @ 150A as it should be.
It might have something to do with the ac load type and PF and the way the inverter reads it and powers it.
This is possibly due to the ve bus dc reading as well. Not sure just spit balling.
Do you have SCS on?
Hello Catalin, After reading your issue regarding DVCC limiting the amps to your battery bank that I find it very interesting. I have 9 MPPTs 4 RS 450/200. 4 MPPT 150/70 and 1 MPPT 250/60. After reading about DVCC and understanding the pro or con I thought there is too much automation. So what I did is to put limit on each Solar Charge Controller. My system is running for about eight months without any issue.The way Victron System is running I love it. I am not sure the way I put limit on the MPPTs is the right thing to do. The system is working great. Good luck.
I did the same from the begining, 150A for rs450/200 in order to have less than 6-7A on each pv string. When is needed i can go up to 13A per string on winter or so.
I checked again today and confirmed that the behavior occurs only when the water heater is on. With other loads, the charging current stays exactly at the DVCC limit. So I assume the behavior is induced by resistive load.