Since the beginning I’ve noticed that mppt isn’t reaching the current I’ve set in DVCC (120A), even if there’s no load applied on system. For instance, DVCC max charge current is 120A, but battery is charging up with ~95A. There’s no restriction from PV perspective, but if I go up with DVCC settings, the charging current is growing proportional but never reaching the value I’ve set. There are no faults or alarms on the system.
Do you have any other Victron “DC charger” in the system, connected on the same network, that “shares” the DVCC “universe”?
An MPPT or Multi RS or even “active” Multiplus chargers… ?
The actual MPPT current limits : 450 = 160A, 150 =45A, 250=100A. But last two will barely reach 800W(2 pannels) and 1.5~1.6kW(5 pannels). If the current distribution is by percentge as you explained, then makes sense. Thanks!