I don’t know the EasySolar or Fronius, but a Victron Multi Solar RS has two MPPT PV inputs, a battery connection and 6 kW. The PV power goes directly into the battery, without any DC-AC-DC conversion taking place.
Yes!
The Multi RS has the advantage of being configurable as a grid-tie inverter and of being able to operate without a battery.
Its biggest advantage is that it allows you to build an expandable system, as it will be very easy to add batteries later on by simply changing a setting!
Another advantage is that there are no communication issues; it communicates very well with the rest of the Victron system.
Its specifications are similar to those of a PVI 6, but a little lower. You’d need to check whether the panel voltage and current are compatible.
A Fronius would be a very simple replacement, with no need to rewire, or rearrange your string. An MPPT isnt a bad idea but it might well require significant alterations to your existing panel layout and wiring.
When your Aurora eventually fails, it will very likely be one of the grid relays that requires replacement, this is a relatively simple task that is widely documented.
Thanks, Thierry.
To get back to my original problem, I switched back to “Optimised without Battery Life” mode, without the ESS tab. During the evening and overnight, the battery discharged to power the house as normal. When I woke up at around 7 am, it was still at 62% charge, and the indicators on both batteries were at the same level.
I turned on the kettle (2000 W), and then disaster struck. It ran for 4 to 5 minutes. The charge dropped to 34%, and the slave battery ran completely flat, triggering an alarm. The master battery stayed at its “previous” level.
I don’t understand what triggered it. Above all, it makes me doubt the information being sent to the Cerbo. Losing 28% (according to the display) in 4 minutes is strange.
The two batteries were bought 8 months apart. I don’t know whether the firmware could be a factor…
The BMS recalibrates the SoC based on certain voltages. If a battery gives out (one or more dead cells), it’s not unreasonable for the SoC to suddenly drop.