Configuration Cerbo GX - ESS

Hello,

I was finally able to commission my installation last Friday, 9 October. It involved taking over and bringing the previous owner’s installation up to standard.

You can find the installation diagram below:

However, I’ve noticed that a very large proportion of my solar generation is being fed back into the Enedis grid instead of charging the batteries.

For example, today at 11 a.m. the solar output recorded by the inverter was 2797 W.
In VRM, I see the following:

And at 1:12 p.m., the ratio is even worse:

Overall, one third of my total generation is used to charge the batteries, 10% is consumed by the house, and the rest is fed back into the grid.

This is something I’ve noticed from the outset: the batteries aren’t fully charged when generation stops, and a lot of power is being fed into the grid.

I’ve also noticed that my two Pylontech batteries aren’t at the same charge level. The master battery is always “two lights” ahead of the slave.

As I’m very new to the Cerbo, could you tell me whether this is normal operation or whether I’ve configured the Cerbo incorrectly?

Here’s what I have in the charge control settings:

However, in the battery settings, the CCL is limited to 20 A, whereas the maximum charge current is 100 A:

Thanks for your help, and have a lovely day.

Derry

The problem is that the CCL is sent by the battery, so there’s probably an issue on that end.

Thanks, Thierry.

I was looking on another forum. A user had the same problem, and they were advised not to enable BatteryLife.

But it’s enabled on my system:

If so, what should I enter? Optimised without BatteryLife?

There is lots of discussion about batterylife yes/no.
I would start with turning off DESS and sets the charger to “keep batteries charged”, see if the batteries will reach 100% and then keep it there for a few hours to make sure all is balanced out again by the BMS.

You could see if you can find min and max of the cells. I believe pylontech bms shows that somewhere in the cerbo.

In any case, whether it’s Battery Life, DESS or something else, the CCL sent by the battery still needs to be correct, because that’s what the system uses as the basis for regulation. That isn’t the case here.

Battery Life is a function that doesn’t manage charging; it manages the discharge SOC threshold, so it has nothing to do with that. Its purpose is to encourage a full charge by allowing the battery to discharge more or less. Basically, if you don’t charge to 100%, it raises the minimum SOC so there’s less battery capacity to make up the next day. But it doesn’t affect battery charging.

Nice setup @Derry

Just a sidenote, it might be a diagram error but please have a look at actual setup, the two batteries should not be directly connected together as you already have independent busbar connections and fuses.

Thanks, Thierry, for your reply and for shedding some light on this.

How can I adjust the CCL sent by the battery? At the end of the day, I’m only at 60%. I have one battery that’s almost full (5/6) and the other almost empty (2/6).

I called the company that sold me the batteries, and they advised me to switch to “keep batteries charged” mode and wait 48 hours to rebalance the internal cells in both batteries. I’m trying this, but it doesn’t seem to be charging much more.

Thanks, Radunre. The diagram is wrong: there is no direct connection between the two batteries (the two circled diagonal cables).

I’d reused the “classic” Pylontech wiring diagrams and forgot to remove those two when I added the busbars and isolators (one per battery) to my setup.

And what percentage is your battery charged to now? Is it slowly increasing, and what’s your CCL now?
I think you need to turn off DESS to set “battery charged”.

65% at 4am… and CCL still at 20A…

I assume DESS stands for Dynamic ESS?

If it’s accessible via Menu > Settings > Dynamic ESS, then it’s never been configured

If it’s a setting in the Console, I’d appreciate the path to it, as I can’t find it

I’d probably try to find out which battery is sending the nonsensical readings, and why.

I’d probably take one battery completely out of the system for a day at a time (remove the battery fuse and disconnect the BMS cable).

If that doesn’t help clarify things, you could run a battery parameter analysis via a BMS firmware update or through the console. Basically, it’s just a decimal point in the wrong place.

“On the GX, you can find DESS mode under Settings → ESS → DESS → Mode”
If you can’t find a DESS option, then you haven’t set any of it up, so you’re all good. ESS should be set to
(note: I have a Multi Solar RS, so the path in the screenshot is incorrect)

Plus what @stadtrand says, because then you can work out which battery might be causing problems.

If the voltage difference is too large, it’s best to disconnect the batteries and charge them one by one using a bench power supply or something similar.

It can’t be adjusted; that message is coming from the battery, so you’ll need to check with the battery manufacturer.

The battery may be unbalanced, which could be causing this. However, 24 hours isn’t long enough to balance it out — it can often take a week.

Personally, I’d leave just one battery connected, put it on a maintenance charge until it reaches 100%, then disconnect it and do the same with the other one. If both batteries reach 100%, reconnect everything. If one of them has a problem, you’ll need to request an after-sales service repair!

Good evening, Thierry,

It does seem to be a battery imbalance. The batteries reached 100% charge yesterday at noon.

The supplier advises me to leave the “keep batteries charged” option enabled until Friday.

I have a follow-up question, since you’re part of the Victron team: could you please tell me which Victron model would be suitable to replace the Aurora Power-One inverter in my installation? I have a theoretical 6,000 Wp on the roof, and the current inverter has an output voltage of 230 V and a nominal output power of 6,000 W.

A Fronius Primo 8.2-1 is my suggestion.

Thanks, Sean. But isn’t there an equivalent from Victron?

Your Aurora is a grid tied inverter, there is no like for like Victron product.

Thanks, Sean. I thought the EasySolar II-GX could be used as an inverter/charger, but apparently that’s not the case.

If the inverter fails (the system is over 10 years old), Fronius is an option, or I could replace the system and add an MPPT, such as the RS 450/100. Is that right?

In my oppinion, the ideal combination is a Fronius Primo 6.0-1 that will mostly help with day to day AC consumers and a future expansion with an MPPT to help charging and eventual black start.