As far as I know, with an external transfer switch you need the CT’s for safety as is drawn in the diagrams. When the TS is switched off and the MP-II measures any current, it will switch off the system to prevent accidental back-feeding in the case of grid loss. I can not use the EM/ET here, as it is not certified for that.
The EM/ET is solely for ESS use. You’ll need them both in the case of an external transfer switch.
Sorry, yes, it is a requirement for the ETS solution, I forgot about that part, it is hardcoded into the software.
You don’t get more accurate than an EM but it sounds like its more about response time of measurement.