I have two Renogy 200w panels and may have room on the roof to add a third to my design, but the Voc = 37.44, Vmp=31v, Isc=6.85. If I use these in series, I will exceed the 100v limit of the Smartsolar 100/30. Vtot=112v > 100, correct?
If I use three in parallel, will my Vmp of only 31v be enough for a 24 volt system, that is, will it meet the threshold of Vbatt+5 with less than full sun to turn on and charge the batteries?
Is using the SmartSolar 150/35 the only way to work with these three panels?
In addition to the reply relating to series layout if you put them in parallel then it is the Voc that is important for the start up because at start up, you have no current flowing, the controller has the panel open circuit, so the 37V should be enough to start so you could use the 100/30 in this case. The 150/35 will give you more flexibility.
Thanks for that. Would there be other benefits reaped from the extra investment for the 150/35 such as running cooler? I read that having PV 20v higher than Vbatt optimized the efficiency (?). Are these considerations worthy?