AC Loads with AC connected solar

Hi,

I’m just installing my first system. Multiplus ii 48/5000/70, single phase 230V. System is running in ESS mode with a grid setpoint of 20W and all appears to be working as expected apart from the indicated AC Loads power value.

I have a separate AC coupled solar inverter connected to the AC input side of the Multi along with all the house loads so nothing is connected to the AC out 1 or 2.

The first issue is that although I’ve set the position of the AC loads to be “input only”, they’re still shown on the output side of the Multi in the system overview (and on the VRM).

The second issue is that, because the solar is AC coupled, the AC loads power value is not showing the true power value. It’s showing the effective load power as seen by the system (true load power minus the output of the solar system). Is there a way to configure this to show the true AC load power (grid power + battery output power + solar power)?

Just to add, I’m using a CT for the grid measurement connected directly to the CT input on the Multi. I’m using a “40A Victron Current Sensor” to monitor the Solar production via AUX#2 input.

Your system does not know there is a PV inverter, you need a dedicated current sensor or meter configured for the right PV role (unless it supports modbus).
Suggest you brush up on the relevant manual sections or even Victron Energy - Victron Professional
The gui has a logical layout that won’t change for AC loads if they are only on the input and there is no AC out (critical) loads.

Hi Nick,

I’m using a 40A Victron Current sensor connected to AUX#2 of the multi to measure the PV production. This is configured as “PV Inverter on Input 1”.

Can you show the specific configuration of that sensor?

Sure, this is the info via the GUI. This was configured initially via the Current Sensor Assistant.

ok great. Getting myself in a knot here with the UI display.
How is the multi metering the grid? Where is it placed?
Maybe provide a diagram.

Hi Nick,

Thanks for getting back. I’m using the standard 100A:50mA Victron CT. This is around the live meter tail inside the consumer unit / fuse box. This seems to be measuring fine. Grid CT setting is “Inverter/Charger”, not “External” (I have a 3 pin connector block for the CT connection).

I was going to use AUX#1 for the PV current sensor but I’ve set the grid code to UK:G98 which then forces you to use AUX#1 for the “Disable feed-in” signal. Like I say though, the actual indicated power of the PV appears correct using this meter and AUX#2.

I can understand if the Multi doesn’t know the AC PV power it will have to calculate the AC load based on its inverting output power + grid power. If however it knows the AC PV power and knows that it’s grid-tied on the input side, the AC loads should be the sum of all three (Grid + PV + Inverter output).

As an example I’ve disabled the ESS in the screenshot below. There’s no inverter power in this case so AC loads should equal Grid + Solar but they don’t. The Solar power is not being added onto the AC loads power.

Could the Status of the “PV Inverter on input 1” being “Startup(0)” be the problem? This code seems to suggest that the device is not ready yet which may explain why the system isn’t using its power reading in the AC loads calculation?

What firmware version combination do you have there?

Can i make a small suggestion.
Try GUI v1 and see if it is s display issue?

Hi,

Firmware is 3.62 (MP2 GX).

The two versions of the GUI show the same PV production values however the grid power is different for some reason. If I had to guess I’d say the PV is being deducted from the grid reading in V1 but not in V2? I’ll have to confirm this once I have zero PV generation.

System was in the middle of a scheduled mains charge when I took these…

This is the gX

What version is on the MP2?

Hi,

It’s 2623498 (shown in the VRM devices list).

Something I have just noticed is that the PV generation value is stuck at 172W. This was definitely updating earlier.

UPDATE… rebooted and now PV power value is updating again.

I’m hoping you’re going to tell me FW 2623498 has issues! :slight_smile:

No more 498 is old.

I would update the inverter (and reprogram it) and then go from there.

Switch off auto updates on the GX too.

Thanks for the info LX.

Looks like v498 was October 2022 so fingers crossed an update will help.

Job for the morning. I’ll update this thread tomorrow…

I’ve now updated the MP2 to v556 but no change re the AC Loads power value from what I can see. The PV generation connected to AC In-1 is not being accounted for in the AC loads power value.

Below shows the system with ESS disabled so no inverter power. The grid is supplying 326W but the loads in the house are being supplemented with 201W of solar so the true AC loads value should be the sum of both, 527W.

The grid values show in the VRM are even more confusing. The L1 value shown in the Grid power box is correct (-38W due to higher solar so feeding-in slightly) but the main value of -608W makes no sense. Is this the 239V x 2.5A shown in the L1 section?? If so, these power values are mixed up.

Just to further clarify the issue. The following screenshot shows the system running with ESS enabled and an excess of PV generation.

AC Loads is shown as 0W where it should be GRID + SOLAR + INVERTER. In this case that would be 17 + 974 - 469 (negative because the Multi is consuming power to charge the battery). The result should be 522W.

The inverters read in rms, rms can be influenced by power factor.
If something isn’t adding up, then that would be something to check.

When the system is on, there is never a situation where the inverter and the system does not have self consumption and losses due to heat. So numbers will never be exactly on the dot.

Do you have anything measuring the grid feed before the pv inverter?
If i am understanding correctly the pv inverter is on the input and is being measured by the system, but unless i missed it being mentioned how would the system know what is being pulled from grid? Or do you have a grid ct and a ct for the pv inverter?

@Chris78 Did you enable the CT for the grid metering on the multi?

Hi LX,

I solved the issue just last night. It’s because when I ran the AC Current Sensor Assistant, I’d set the position of the PV Inverter to “On AC input 1 of this phase” which is correct as my PV is connected to AC-In-1 along with all the other loads (grid parallel mode with nothing connected to AC outputs).

In this configuration however, the system does not add the PV power to the AC loads power like it should do. It also leads to the PV power being shown as grid export in the VRM for some reason.

I have Settings > System Setup > AC System > Position of AC Loads set to “AC input only” so with the PV also configured as “On AC input 1 of this phase” the PV will supplement the AC loads and as a result, the AC loads power calculation should be GRID + PV + INVERTER. As I say though, the PV power is not included which I assume is a bug.

The fix is to set the location of the PV Inverter to be “On the output of this phase” in the AC Current Sensor Assistant.

In this case, what is measuring the grid?