I have an on-grid system composed of a SMA Sunny Boy (with SMA Smart Meter) and solar panels.
Recently, I added storage capacity consisting of 2 Pylontech US5000 batteries, a Multiplus 2, 3kW, and CerboGX. I also installed ESS.
I have established the communication with the SMA inverter, and it is seen by the CerboGX.
All software, firmare is up to date.
The Country Grid Code is set.
However, in “Optimized (with or without battery life)” mode, the batteries are not charged (from PV excess).
Instead, the excess PV is sent to the grid.
Also, in this mode, the loads discharge the batteries instead of taking energy from solar.
To charge the batteries I have to manually force the “Keep batteries charged” mode, which is not ok!
I have attached screenshots from my system.
Can you help me to find the problem?
Do I need another meter or the SMA Smart Meter is enough?
As can be seen the batteries are not charged (from PV excess).
Instead, the excess PV is sent to the grid.
Also, the loads discharge the batteries instead of taking energy from solar.
Generally, do you feed in or not?
What’s the configuration on the Cerbo’s Grid feed-in and on Peak shaving?
Did you played a little with Grid setpoint?
If you try to force a charging with the ESS schedule, will it work?
Again, ESS schedules shown in the last picture in your first post, last option under ESS menu on Cerbo.
what length / size wiring and how are things connected?"
But I cannot enable SVS. It is “forced-off”.
Also, what wiring is he referring to? Battery wiring? I used some 25mm^2, 2m long cables that come with the battery. But, on the red cable I put the 250 Amps fuse and I extended it by 1/2 meters. So, black one is 2m and red one is 2 1/2 meters long. Does this matter?