Hi Everyone!
I’ve got a ABB B24 352-100 Silver meter for a project in the near future, On site we are using ESCT T24 100/5A CT clamps. these are already installed on site.
I want to build a test setup in the shop, to verify the system works as expected. The only CT clamps i have avilable are the ones that come with the vm3p75CT meter from Victron (Tokin C-CT-0810-65-01) And i was wondering if i can use these clamps for the test setup, and if so, what ratio i’d need to put into my B24 meter.
I get confused since the specsheet of the Tokin clamps states that the clamps themself work on a 1:3000 ratio, so that gives me ~0,022 A on the secondary side on max amperage. Is this a misunderstanding on my side?
Thanks in advance!