The configuration here is used for an RV. It is split-phase parallel of 4 Multiplus II 48/3000’s. The slave of L2 is showing negative wattage when trouble shot with L1 master and L1 slave to verify the problem. L2 master works fine with L1 master and L1 parallel. If the 4 units are running as a whole as configured, when grid comes on, Cerbo GX shows L2 AC loads drop. The wattage drop varies with the load applied. When the grid is dropped and it stays in Inverter mode, L2 wattage returns to normal.
There is no configuration I’m aware of that would cause this. Ground relay is verified as only on L1 master. Both sides of the AC in and out have identical length and gauge. Here’s the thing. I’m not so much worried about fixing this inverter because I’m pretty positive that it just needs to be repaired. I am more concerned about something in the VE bus monitor. While I was troubleshooting the negative AC thing I found that when it is in inverting mode, it indicates L1 and L2 out of phase. When the grid is turned on, it accepts the connection and VE bus drops the “not in phase” warning. I verified this in every split-phase configuration: L1 and L2 full units, L1 Mast and L2 Mast, L1 Mast and L2 Slave, L1 Slave and L2 Mast, L1 Slave and L2 Slave. When the grid comes on they’re on in phase and inverting is out of phase. All connections were checked and are connected to the right phase.
VE configure 3 is up to date and all units have updated firmware.
Is there a bug in VE configure causing this? Without an oscilloscope I’m not sure of a way to check the phase. The in junction box is identical to the out junction box. I doubt the bad L2 slave inverter is causing this reading. That’s the only thing I have not done is remove the connection from each junction box to see if somehow it’s influencing it. Ideas?