I have two Multiplus II 24/3000 2x120 units connected in split phase configuration feeding an Autotransformer for load balancing. I have 50 amp 120/240 split phase input as my shore power. L1 of shore power is connected to L1 AC input of the master phase 1 Multiplus while L2 of shore power is connected to L1 AC input of the slave phase 2 Multiplus. When inverting, the Multiplus units properly show L1 and L2 AC loads as expected in VRM, Victron Connect, and the local portal. However, when on shore power only L1 AC input and L1 AC loads are shown. L2 input and loads are at 0 watts. I know this is incorrect because I have power on L2. I have a Hughes Power Watchdog surge protector wired into my shore power input before my Victron system, and it shows loads on L1 and L2. I am able to operate appliances on L1 and L2 as well as 240v appliances on shore power.
Is there some setting I have to enable for proper load reporting from the Multipluses? I have a virtual switch for ignore AC input setup to maximize usage of my solar array. Without L2 loads reporting, I am worried my excess load condition would not trigger a switch back to shore power. This may not be too big of a deal since I have the autotransformer for load balancing. However, I would like accurate power usage statistics because by only reporting L1 loads my true usage will be about double what VRM logs.
Did you ever find a solution to this?
Unfortunately not, still trying to figure it out
I plugged a pair of wired headphones into the current sense jack on the multi handling L2. Apparently there’s a spring contact in there that can come from the factory bent out of place causing a short. After plugging the headphones in a few times, it seems to have fixed the problem and I now have readings on L2.
Glad you got it figured out! How did you set up your virtual switch to ignore AC input?
I am using a MK3-USB interface to adjust the settings using the VictronConnect App on my MacBook Pro. I selected the “AC input connect based on load” slider and it works correctly for the “Connect when load is higher than” setting. The problem occurs with the “Disconnect when load is lower than” setting. The “Disconnect when load is lower than” setting only uses the wattage from L1. So even though the load in L2 is higher than the set amount in the “Disconnect when load is lower than” setting (L1 at this time is below the set threshold), it will still disconnect the AC input. If you are using the victron connect app do you have this issue?
I copied this procedure: Example: ACin ignore timer using the CCGX Generator auto start/stop function [Victron Energy]
I have a Cerbo GX that I use and treat shore power as a generator. There are settings on the Cerbo to turn the generator on/off based on AC load, SOC, etc. I have it set to monitor AC load and switch the generator (shore power) on when the load on the highest phase reaches my set value. Similarly, I only have it turn off shore power when the load on the highest phase is below threshold. This way I can switch my conditions on the fly from the remote console vs having to connect my laptop via MK3-USB to the multis.