Inverters with 4105 manufactured after 2011 must reduce their power output as the frequency increases. The country code often includes something like :2011 or :2018. However, according to 4105, the minimum is reached at 51.6 Hz; at 51.7 Hz, the inverter should disconnect.
Planning: 3 MultiPlus 5000s, 2 Pytes V5s.
ESS, on-grid; since it’s three-phase, after the meter it goes into AC in and then from AC out to the house distribution board (without any changes).
This means the Sungrow is connected to AC out.
It’s specifically about frequency control and whether the Victrons can potentially regulate the Sungrow down to 0 in emergency operation.
The Victron apparently has an upper limit of 52.7 Hz — at that point, the Sungrow must no longer supply anything!
Can the Sungrow do exactly the same?
Does anyone have this exact installation?
The two Pytes batteries appear to be too small for the system. In addition to the charging and discharging power, the Factor 1 rule must also be taken into account.
You can see how far the MultiPlus can increase the frequency in Demo mode using the Fake Device in Ve.configure.
You should find the remaining values in your solar inverter’s documentation.
The MP2 throttles the inverters. According to observations, it also does this when operating in island mode and the grid returns after a simulated power cut. It can then take up to 15 minutes for the inverters to ramp back up to full output.
apparently, no one has any experience with this particular Sungrow.
Neither do I.
Under specification AR-N-4105, it must be controllable; otherwise, it would not be permitted to operate on the German/European grid.
Victron uses Frequency-Watt for off-grid operation, and it can even be configured with VeConfigure.
I have Hoymiles connected to ACout. It works.
How it works: the MP2s increase the frequency, according to the frequency. Conversely, the power must be reduced by up to 60% in a linear relationship with the increase in frequency. The system then shuts down.
When the frequency is reduced (Recovery Frequency), the inverter switches back on after checking the grid (MP2 island grid). The Ramp Rate defines how quickly the power can be ramped up again.
The additional information about your system design concerns Victron’s requirements for making it work. If you do not observe the important design rules, your system could catch fire because the energy cannot be absorbed during the changeover period.
The MP2s must be large enough (1:1 ratio)
The batteries must be large enough (3–4 ratio)
So, in short:
We don’t know; it should work according to the approval.
Your system has not been designed safely—dangerous!
Greenakku sells the MP2 48v 5000 set in a three-phase system as a 15–30 kWh storage system, which can be expanded modularly.
I would have to consume electricity for 2 hours at full load (12 kW continuous output) to run it flat. The Liontron batteries are specified as having ideal charge/discharge currents of 0.2–0.5C. 100 Ah = 20–50 A. At 12 kW, the discharge current would be 250 A, i.e. a maximum of 50 A per battery.
Bei Pytes ist die Doku ein wenig dünn, daher nehme ich meisten die Werte von Pylontech und rechne die auf die anderen Batteriehersteller um.
Für Pylontech wird PRO Mp2/5000 100A = 300A Mindeststrom empfohlen
Die Pytes V5 haben 75A sprich für die 300A mindest 4 Blöcke
These minimum battery sizings are required for reliable operation.
An example of minimum system sizing based on the US2000 battery module is below. Each battery module is approximately 50Ah at 48V, can provide 25A continuous charge and discharge and 100A peak for 1 minute.
Inverter / Charger Model
Inv continuous watts @ 25 degrees
Inverter peak watts surge rating
Number of Pylontech modules
Battery continuous discharge watt rating
Battery peak discharge watt rating
Multiplus 48/500/6
430
900
1
1200
4800
Multiplus 48/800/9
700
1600
1
1200
4800
Multiplus 48/1200/13
1000
2400
1
1200
4800
Multiplus 48/3000/35
2400
6000
2
2400
9600
Multiplus 48/5000/70
4000
10000
4
4800
19200
Quattro 48/8000/110-100/100
6500
16000
6
7200
28800
Quattro 48/10000/140-100/100
8000
20000
7
8400
33600
Quattro 48/15000/200-100/100
12000
25000
10
12000
48000
Weiter geht es mit dem AC coupling
Minimum battery capacity
Besides the relation between installed PV Power and the inverter/charger VA rating, it is also important to have a sufficiently sized battery. The minimum battery capacity depends on the type of battery, lead or lithium.
Note that, besides the minimum battery capacity, the mentioned sizes are often also the most economical battery size. In case used for self-consumption purposes that is. In case the goal is to increase autonomy, of course installing a large battery increases the system autonomy in case of a grid failure.
3.2 Lithium batteries
1,5 kWp installed AC PV power requires 4.8 kWh of battery storage:
** 100 Ah at 48 Vdc**
Each additional 1.5 kWp of AC PV will require an additional proportional 4.8 kWh increase in battery storage.
Ich komme auf auf über 8 Batterieblöcke für die 12,5 KW AC PV
It’s enough for a lorry to take out a medium-voltage power pole. That’s already happened here in town, and the power went out.
If it happens in summer and the batteries are fully charged, the curtailment is supposed to prevent the voltage from rising too high.
And why keep your fingers out of it? Because it doesn’t work anyway? It does; that’s the required standard.
I’ll keep this factual — but unfortunately, most people simply have no idea about it.
I work extensively with UPS systems at large events.
A power cut — one that only occurs once every five years or so — means that even quickly installing three MP2-5000s simply isn’t enough; there is much more to consider.
There are some very unusual scenarios — whether it’s switch-mode power supplies with high inrush currents, devices that can’t tolerate the 20 ms switchover time, loss of internet connectivity, and so on.
Simply installing three MP2s and thinking you’ve bought yourself absolute security is nowhere near enough.
At these events, we deliberately don’t use Victron as a UPS, even though it’s an excellent system.
It isn’t suitable for that purpose — but that also stems from it having been designed for a different use case.
If I need a UPS for a large-scale event, then we’re talking about entirely different dimensions.
And in that case, I go straight for autonomy for the transmission equipment. I don’t want a glitch with the link going down for 4 seconds while the frame is rebuilt (MPEG-4).
For a private household, the MP 2-XXXX units are sufficient. And the issue here was whether I can use the frequency to curtail µWR at the AC output or not.
No, this wasn’t about data centres, concerts or other large-scale events.
The question was simply: Will my system burn out, or potentially not…
And ignoring that essentially means, in the worst-case scenario: battery BANG