150/70 MPPT Equalization current percentage not working
Max charge current was set to 70A
Equalisation current percentage was set to 10%
After completing absorption, the mppt was placed into a manual equalization. According to the settings (10%) the current should have been limited to 7A, but the current was not being limited by the equalization current percentage. I tried changing the equalisation current percentage multiple times over to no effect, in the end I had to change the max charge current to limit current for the equalisation process.
I believe there is an issue with the mppt itself or the software (most recent version 6.18)
max charge current 70A
Equalization voltage 56.4V
Manual equalization in progress as inferred by the “Stop” option
Charge current 24.9A (should be max 7A)
Does the battery need equalization? If you do need to use it you could drop the max charge current to 7A till you find a fix.
I already stated that’s what I did/had to do. I’m here to warn others and for Victron to acknowledge and fix the issue.
Looks like you’ve got it all sorted! I can’t imagine there are too many people still running 48V lead-acid systems these days.
What does battery chemistry have to do with this discussion?
Where does it say the setup was using lead-acid?
The equalize function can be used to limit current after absorption for the purposes of balancing LFP, that’s what I was doing.
Just to clarify we’re not really having a discussion here. You made a statement about a fix you found, but when I asked whether your battery actually needs equalization, you didn’t respond. Equalization is only necessary for lead-acid batteries, which is why I asked in the first place. If you’d answered that, we could have had a proper discussion about it.
see
I hadn’t thought about it that way. Here’s a post I put up the other day. I use Node-RED to drop the DVCC charge current to 2A when the battery reaches 99%. It also gradually reduces the charge current from 100A down to 20A as the voltage rises from 13.6V to 14.2V. I’ve got a bunch of 12V batteries in parallel, and they take ages to settle. This setup works well just another approach to consider.