I currently have a grid-tied solar system using Hoymiles microinverters (AC-coupled). I’m considering installing a Victron MultiPlus-II with batteries to add backup capability and possibly operate in off-grid (island) mode during grid outages.
My question is: Can Hoymiles microinverters continue to operate and feed power into the system when the MultiPlus-II is running in off-grid mode and forming the grid?
I understand that microinverters usually require a stable grid reference (230V / 50Hz) to operate and that not all inverters provide a signal accepted by anti-islanding protections.
Does the MultiPlus-II provide a sufficiently clean and stable grid reference to keep Hoymiles microinverters active in island mode?
Yes, they do. But they are not ideal, when it comes down to throttling through frequency shifting, iirc they won’t go bellow 50% power, but rather shut off to 0 then.
@dognose - can you tell more about it? I haven;t heard about this issue - that Hoymiles microinverters can’t gradually go down to zero via frequency shifting. If they can go only to 50% and then shut down then it is a real flaw.
Thanks Marc. Maybe they also implemented rate-of-change monitoring. I can see the moment Victrons raised freq in big step Hoymiles reacted immediately and shut down. Wondering what will happen if frequency keeps increasing gradually, with no step changes.