I am running a pure Off-Grid system with a MultiPlus-II 5000, a Cerbo GX, and a CAN-bus managed BMS (DVCC enabled). I do not use ESS.
Recently, I experienced a prolonged fiber/internet outage overnight. During this outage, the MultiPlus-II briefly shut down / lost power output almost exactly every 60 minutes, which triggered connected loads.
Key observations:
In the Venus OS notifications, I found the entry: BMS connection lost / Multiplus-II 5000/70-50.
Normal GX rebooting during normal operations does NOT interrupt the MultiPlus-II output.
As soon as the internet connection was restored, the hourly power interruptions completely stopped.
The issue occurred on both v3.81 and v3.79.
Logs show connmand failing the online check (Online check failed for Wired) and falling back to Link-Local IP (196.254.x.x), triggering watchdog0 activities.
System details:
Device: Cerbo GX (HW 2, FW 5)
Inverter: MultiPlus-II 48/5000/70-50
Setup: Pure Off-Grid / DVCC active / No ESS
It appears that the hourly network/NTP/VRM retry loops during an internet outage cause a brief freeze on the dbus or CAN interface, leading to a momentary BMS signal loss and subsequent MultiPlus safety trip.
Could this be looked into for future Venus OS maintenance releases? Let me know if further dmesg/system log dumps are required.
You have likely configured an automatic reboot on connection lost in the GX VRM settings. This should not trigger any BMS lost errors as it is a normal reboot and the GX has a timeout for this.
You don’t document what your BMS or battery is or if any modifications are loaded.
The BMS lost could not be caused by a conventional lost comms initiated restart, those happen every day to many users.
This is well documented in numerous topics available via search.
As a new user, it would have taken a fraction of the time finding this existing information, than was spent having an AI format this post.
Thanks, Nick, for the information!
I hadn’t realised that an automatic restart of the Cerbo GX causes the MultiPlus II to disconnect from the grid.
If, for example, I do a firmware update and the Cerbo GX restarts, or I click Restart on the Cerbo, I never have a power cut.
Apparently, it’s different when it restarts automatically after an internet outage.
It does not. Something else is happening. Some features like dvcc will stop and the mode may change but the timeout is so long a reboot can never cause an outage, unless you have modified the OS or forgot a usd drive is connected (or an SD card with a firmware file on it).
If you have asked an ai to work out what might be happening, it will be telling you nonsense. Rather source the information here from other user reports and questions.
Remember, we can shutdown, fully update the OS, and still not timeout the BMS. There is no technical difference between a reboot, whether done manually or triggered by an update or the watchdog.
That’s interesting…
There’s no USB drive connected or SD card inserted, and nothing has been modified either, yet I had four brief power cuts during the night, an hour apart, just as the Cerbo GX was configured to restart when the internet connection was lost.
I’ve now disabled the restart so this can’t happen again if a farmer in Upper Austria drives a fence post into a fibre-optic cable and the power goes out here in Lower Austria.
Go check the boot logs, you should be able to get timestamps from the watchdog rebooting to the services being up again. The GX would need to be offline for some time for the devices to timeout the bms.
are there some Scripts like NodeRED running? I had a simmilar problem, was my fault in the end: a NodeRED Script couldn´t reach the internet, in the end system load got to high, watchdog forced a reboot
Quite a bit is running in NodeRed, including a lot of things involving external access.
I checked the boot log and, according to that, the CerboGX hasn’t restarted. The only restarts were when I changed the firmware version, because I thought the latest firmware might be the cause. Basically, it was only the MultiPlus II that had a hiccup every hour.
Restarting is now disabled in VenusOS. Now I can only simulate a longer internet outage again and see what the Multipus II makes of it.
Unfortunately, I can’t access a public network here.
We had a thread about this recently. Someone was also running a lot of things through NodeRed that need internet access, and during an internet outage I think it filled up the storage or something, which caused problems too.
True, but this adds the ability to overwhelm resources, triggering the watchdog, or to fill the filesystem and any number of other potential issues which are not factored into testing.
So when something unexpected happens, step one is to turn off any and all customisations so the fault can be isolated to the OS or to custom code.
This is the first thing we ask people to disclose, as 99% of reports are down to integrations the end-user has made.
It saves a lot of time wasting.