WiFi connections fail on Raspberry Pi devices running Venus OS when the access point has PMF (802.11w / Protected Management Frames) enabled, even in optional mode. Issue confirmed on v3.66 with Compute Module 4. Connections only succeed when PMF is completely disabled on the AP.
Venus OS v3.55 may have been the last version with stable wifi for Raspberry Pi Zero W 2.
Related Issues
Affected Devices
Raspberry Pi Zero W 2 (Broadcom BCM43436, 802.11b/g/n)
Raspberry Pi Compute Module 4
Both tested on Venus OS v3.66 with identical PMF connection failures.
Symptoms
WiFi shows “Connecting…” indefinitely
Never obtains DHCP address
AP side logs (OpenWrt hostapd) show:
Device authenticates successfully
Device associates successfully (visible in station dump, good signal)
WiFi connectivity with PMF optional worked on previous Venus OS version (likely v3.55). After upgrading to v3.66, connections fail with PMF enabled on the access point. Testing with Compute Module 4 (different WiFi chip) on v3.66 showed identical failures, confirming this is a Venus OS software regression.
Workaround
Disable PMF on the access point:
OpenWrt: option ieee80211w '0' in /etc/config/wireless
Note: The Venus OS upgrade to v3.66 happened at the same time as I was changing access points, which initially caused confusion about whether this was a router compatibility issue or a Venus OS regression. Testing with the Compute Module 4 on v3.66 confirmed it’s a Venus OS issue.
@and Thanks for the info on how connman/wpa_supplicant handles PMF under the hood.
A couple of things I’m trying to understand though. The original issue is specifically about v3.66 failing with PMF set to *optional* on the AP, not required. If wpa_supplicant has PMF disabled by default (as you describe), then connecting to an AP with PMF optional should still work, since the AP shouldn’t force PMF on a client that doesn’t support it.
Also, you mention 3.67 specifically. Did something change between 3.66 and 3.67 related to this? I don’t see anything in the changelogs about connman or wpa_supplicant changes. Are you saying the behavior is the same in 3.67, or that something was addressed? Would be helpful to clarify what you’re suggesting as a path forward here.
Just saw your edit. That’s helpful, thanks for digging into the defconfig. So wpa_supplicant is compiled without CONFIG_IEEE80211W entirely on the honister branch. That would explain why PMF required fails for sure.