Venus OS v3.55 display L1 and L2 loads?

I have 2 multi 12/3000 hooked up to RV with 110v leg going to each inverter from the generator which is a 8.5k. I was told that there was a update that would allow me to see L1 and L2 on the main page (like it shows up for split phase). Currently have INV 1 wired to vebus port and 2nd inverter wired into the USB via MK3.
System is currently wired as 2 independent inverters due to the generator being a dual 110v.

As it is unclear here, are they programmed as split phase or do you have 2 totally independent/different inverter systems?

Techniclaly they are not L1 and L2 if they are not programmed as one ve bus

1 Like

The only update that I have seen coming is in the current V3.60 beta test firmware for the new ui. Searching the changelog has not produced anything else.

  • For systems having a second VE.Bus System, connected using an MK3-USB, DVCC parameters may now optionally control all systems. A new setting has been added to enable this; disabled by default.